S

South Spark

Installing under sink water heaters. Each is on its own circuit and could be isolated for maintenance at the consumer unit. Do i still need to provide local isolation e.g a 45 amp dp switch ?
 
Last edited by a moderator:
no.... unless manufactures instructions stipulate fitting one.
 
No, but it could be seen as good practice to do so

Edit: and as Tel said, check the instructions.
 
The problem comes of course with installing switch gear in Zone 2 - rock and a hard place.
 
If you have RCD's installed, I would always recommend DP isolation, and could you put this outside the room?
 
If the means of isolation is remote from the equipment under maintenance and therefore not continuously under the control of the maintenance operative, the supply must be prevented from being accidentally reactivated during the maintenance procedure BS7671:2008+A1:2011 537.3.1.2 This might be achieved if isolation device is capable of being secured in the open position with a suitable padlock or other simple locking method. Whatever the means of isolation it should NOT rely on the maintenance operative having to possess a specialist lock-out kit for MCBs or the like, as that is most unlikely.
 
  • Like
Reactions: 1 person
In assuming you are not going to terminate the T+E into the water heater, you will be making a transition joint to heat-resistant flex,so use an isolator switch. :yes:
 
In assuming you are not going to terminate the T+E into the water heater, you will be making a transition joint to heat-resistant flex,so use an isolator switch. :yes:

Was thinking this myself...your going to have to joint the cable really as they usually require flex in...there usually on FCU's in my experience, out the front in flexible cable...
 
Under the sink is not a zone - unless the sink is within 600mm of a shower! Rectified now just a pain in the arse and to be honest I was looking for a get-out!
 
Neutral is now termed as a live conductor therefor locking off an sp mcb would not isolate all live conductors.

Boydy
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
isolation where circuit serves one item of equipment
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
South Spark,
Last reply from
guest119,
Replies
10
Views
1,509

Advert