Absolutely right Pete. The problem with testing appliances is that even if you have the test set up incorrectly, the appliance may still pass even if it us faulty. It's important to know exactly what you are testing and what parameters are acceptable.
 
Remember seeing someone testing figure 8 mains leads years ago. I asked him what tests he was doing. He didn't know, but just pressed 'Test' and waited for it to say 'pass'. I tried explaining how the IR test worked on his tester, but his face remained blank.
 
  • Funny
Reactions: JK-Electrical
Not appliance testing related, but I always note as a limitation on EICRs that the circuit serving an electric hob and/oven is only tested to the main switch (i.e not to the outlet) where appliances would have to be removed to provide access.
You don’t often come across pull out electric cookers anymore!

Agree with testing eicr to isolator. But if pat testing i would test from the outgoing side of the isolator and wander for r2 continuity.
 
Visiting a friend in a council house she said someone would be coming to test her kitchen appliances.
There was nothing to show they had been tested before.

When the person arrived to do the PAT testing, the first thing he did was ring the bell, then disappeared behind the sheds to urinate.

He then came in with his tester and a roll of stickers and started putting his stickers on the appliances.

I asked why he wasn't testing anything and he replied "I'm doing a visual inspection, VISUAL Inspection", as though I was simple and needed the emphasis.

I told him that the equipment had never been tested and a visual inspection required more than just seeing it was there

He said he needed someone to make the equipment available for testing, so I said I'd bring them into the middle of the kitchen so he could access them all he wanted, but he declined.

He then left having been there for a few minutes and couldn't get out quickly enough. I believe he realised that he was out of his depth with me.

His interpretation of visual inspection was looking for somewhere to put his stickers on. That's all he did.
 
Last edited:
Unfortunately there's a lot of that goes on.
 
  • Agree
Reactions: JK-Electrical
When the person arrived to do the PAT testing ... I asked why he wasn't testing anything and he replied "I'm doing a visual inspection, VISUAL Inspection", as though I was simple and needed the emphasis ... I told him ... a visual inspection required more than just seeing it was there ... his interpretation of visual inspection was looking for somewhere to put his stickers ...
It would be funny if it wasn't potentially tragic. Maybe he thought you were foreign so yelling might work :confused:
 
I think he urinated to warm up for taking the p**s. He was arrogant and condescending.
 
  • Like
Reactions: JK-Electrical
Those things make me shiver.

I wonder why they are called widow maker leads.
 
  • Agree
Reactions: ruston
You can isolate the supply all you like, if you leave that widow maker test lead behind on a job it could lead to serious injury or a fatality.
 
Does that so called test lead you have made have the L & N connected at each plug? If so it's dangerous, and needs destroyed and binned. Before you start testing anything get out 2 Fail stickers for your silly creation.
 
I'm seeing double tonight lol. As @ferg said in the other thread, only the earth pins are connected in that one.
 
  • Agree
Reactions: ruston
In the interests of public safety I've removed all posts with images or suggestions of using a 'widowmaker' lead for the purpose of testing. This part of the forum is publicly viewable and I don't want to risk Google indexing any post that suggests a widowmaker lead is a viable option.
 
In the interests of public safety I've removed all posts with images or suggestions of using a 'widowmaker' lead for the purpose of testing. This part of the forum is publicly viewable and I don't want to risk Google indexing any post that suggests a widowmaker lead is a viable option.
Thank you !
 
  • Like
Reactions: 123 and ruston
Mine were all very heavily edited before hitting the reply button. :)
 
  • Funny
Reactions: ruston
City and Guilds 2377 certificate is based on the IEE code of practice and is The inspection and testing of Electrical Equipment. So called PAT testing is a dumbed down term.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
Website
http://www.jkelectricalservices.com
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
JK Electrical

Thread Information

Title
Omission Of Tests On Inaccessible Kitchen Appliances
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
41

Thread Tags

Advert

Thread statistics

Created
JK-Electrical,
Last reply from
oracle,
Replies
41
Views
10,987

Advert