Hi Folks

RCBO or C/U change that is the question!

On the 18th edition the lecturer in a conversation said if the C/U is not non combustible you cant make alterations i.e fit RCBOs for circuits; this ring true with anyone else?
Loads 16 and 17th edition boards nothing wrong with enclosure but also lights (class 1) not protected, feel i should be wearing a mask (pardon pun) advising its a full board change not a C3 fault.

thoughts welcome
 
No alterations to a plastic board(in effect), is that really what a lecturer told you?
 
I think the first question to ask of the Lecturer is provide a document that backs this up.
What they appear to be saying is no alterations or additions to a plastic C.U
So that would prevent like for like replacement of an MCB or even resetting an MCB or replacing a cable into an existing MCB / RCBO.
It might even mean once you switch off the C.U you can't turn it back on unless it's replaced.
 
Is this Lecturer still lecturing or did they find their true vocation at Amazon?
 
In fairness I can see how they got to that conclusion, although it’s a very pedantic interpretation of the regs.

The argument in favour runs; Your work needs to comply with current regulations, so if you replace a light fitting with a set of downlights or add a new point to an existing lighting circuit in a dwelling then you need to provide RCD protection for that circuit. If the old board isn’t made of non-combustible material then that also needs changing because it doesn’t comply with the current regulations and you’re now making changes in the board itself.

@Strima hit it on the head though in the real world.
 
In fairness I can see how they got to that conclusion, although it’s a very pedantic interpretation of the regs.

The argument in favour runs; Your work needs to comply with current regulations, so if you replace a light fitting with a set of downlights or add a new point to an existing lighting circuit in a dwelling then you need to provide RCD protection for that circuit. If the old board isn’t made of non-combustible material then that also needs changing because it doesn’t comply with the current regulations and you’re now making changes in the board itself.

@Strima hit it on the head though in the real world.
Quite, the difference between those of us who work in the real world, having to tell a customer that their new £30 light is going to cost £800 to fit(not going to happen), and those that are paid to pontificate to those wet behind the ears about their interpretation of a badly worded regulation.
 
In fairness I can see how they got to that conclusion, although it’s a very pedantic interpretation of the regs.

The argument in favour runs; Your work needs to comply with current regulations, so if you replace a light fitting with a set of downlights or add a new point to an existing lighting circuit in a dwelling then you need to provide RCD protection for that circuit. If the old board isn’t made of non-combustible material then that also needs changing because it doesn’t comply with the current regulations and you’re now making changes in the board itself.

@Strima hit it on the head though in the real world.
so pedantic but I have not misunderstood as your reply confirms. thanks for the response. appreciate it
 
Quite, the difference between those of us who work in the real world, having to tell a customer that their new £30 light is going to cost £800 to fit(not going to happen), and those that are paid to pontificate to those wet behind the ears about their interpretation of a badly worded regulation.
I don't fit £30 lights or am i wet behind the ears lad.
 
My 2p worth is if, after adding a circuit / making modifications the installation is no less safe, and not worse than a C3 on the best practice guide #4, then it is fine.

For a new installation or a CU change obviously you would not have a combustible box!
 
Two regs come to mind:
Regulation 641.5: For an addition or alteration to an existing alteration, it shall be verified that the addition or alteration complies with regulations and does not impair the safety of the existing installation.

My take on that one is:
1) The addition must meet current regs, including RCD protection if required.
2) Afterwards, the installation should be as safe as it was before in EICR terms

Also 536.4.203 regarding compatibility of parts. Basically use the right manufacturer.

I've done this loads of times to add RCD protection to lighting circuits so I hope he's wrong!
 
this lecturer.does the college need a bog cleaner? that's about his competence level.
 
FFS. Crazy world. I need another couple of beers before I respond.
 
Incorrect. Sounds like something an under qualified domestic installer would come out with before he brutally fits a 60 quid bg split board that by the time he's done is less safe than the original install.
 

Similar threads

D
Replies
5
Views
3K
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
rcbo or cu change
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
e-spark,
Last reply from
MJPD29,
Replies
19
Views
2,381

Advert