LlandrilloSpark

Just wondering if anybody can shine a light on thisI'm working on a 50's bungalow, original wiring, the home owner has basically knocked down a lot of Walls in his house and just stuffed, cut out or taped up various switches, sockets and roses he didn't want.My job along with various other things Is to sort it all out, I'm adding to the existing lighting circuit so I did a EFLI test on 3 roses and 3 switched, all were over 2000 ohms and cpcs are connected in the board and are present at every point.The strange things are whilst 246v exists across L-N the voltage across L-E is about 80, but also what is puzzling me is 20v across N-E, Ze is good and system is TNS , I found all this at 5pm and havnt done IR yet.Cheers
 
Sounds like a combination of using a digital tester with high input impedance and a floating earth /neutral that's not properly connected/bonded. What type of earthing arrangement does the premises have? I would double check the neutral connection at the CU and test the earth bond.
 
Last edited:
CheersWhat I didn't mention was that when I put my fluke t120 voltage indicator across L-E where the lights would normally shoot up to 230, they hovered at the 75 indicator and the digital readout read 80v, but when I put my Megger MIT across it on the voltage range, it measured 230v!!
 
bad connections on neutrals and /or cpc's. check for oxidation in terminations,
.
 
Yes, maybe start with some long lead tests to check your CPC at points along the circuit. - Could be as simple as having caught the CPC sleeving in a termination somewhere maybe?

Dave.
 

Reply to Strange voltages in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I have an unusual issue with a recent rewire I have just completed which I hope you guys can assist with. For background, this is a...
Replies
19
Views
2K
Was fixing a broken twin florescent fitting today and came across something I couldn't work out. First thing I did was measure the incoming...
Replies
7
Views
3K
Hey so just been to see a dad from the little daughters school class who asked me to have a look at his upstairs landing light pendant as his mrs...
Replies
16
Views
2K
Did a kitchen refurb' a few weeks ago. One of the things the client wanted was under cabinet lighting. As the lighting circuit did not have an...
Replies
14
Views
4K
I had a case today where, if I'd not done things properly, I would have ended up with exactly the same outcome, just saved myself half an hour or...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock