i have just done a test on a property and the pfc at origin of installation was 0.712ka. The 3871 mobs have a 6000a breaking capacity. I am a bit confused as I have read something about it always being higher anyway (16ka) for a fuse or main switch 100a or less. Any info here would be much appreciated as I don't want to say this needs to be changed if it doesn't as customer will unlikely get it done anyway and what code would it be if it is a fault. Cheers
 
You have maximum potential current (PFC) of 712A, the circuit breaker can handle a maximum current of 6000A, therefore the circuit breaker will never have to handle a current above its maximum rating and is therefore safe.
Even if the fault current were above 6000A then annex Zb of BS EN 61439 states for the UK that domestic consumer units must be type tested to withstand, as an assembly, a fault current up to 16,000A if the consumer unit is protected at origin by a 100A or less service fuse.
 
  • Like
Reactions: DPG
Don't be too embarrassed OP, even if your maths is flawed, you quest for knowledge is not. Hope you haven't been put off.

I usually get my noughts in a tiswas with Ω, kΩ & mΩ. Mind I also get confused when I get 4 numbers on euromillions, and somehow only get £29 :(
 
  • Like
Reactions: ruston and Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Breaking capacity of 3871 fuse lower than pfc?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Gerry Savage,
Last reply from
Rpa07,
Replies
8
Views
9,306

Advert