Morning everyone,

I am looking for some advice and knowledge to help jog my memory as it’s been a few months since I finished my course and due to health reasons, I had to give up my job on site as a mate and start working for myself after 4 months off work.

This will be the first job I have had that lets me join a competent bodies scheme as they require a “big” job to come down and assess.

Basically, a fella has had a workshop built in the garden and wants it powered up and the old consumer unit in the house is extremely outdated and will be replaced too.

If you could please look over what I intend to do and pin point any mistakes or alterations that I may have over looked I would be most grateful.
The old CU in the house is fitted with B30 and B5 breakers from http://www.gepowercontrols.com

IMG_1541[1].jpg

I would be looking at replacing this with a 11 Way Metal Consumer Unit-100 Amp Switch with a 63 Amp 30mA RCD 2 Pole-Wylex, Two 6 Amp Wylex MCB's, Three 32 Amp Wylex MCB's and a non protected 40 Amp Wylex MCB for run out to workshop.

30m run of 6mm SWA out to workshop and a 5 Way Metal Consumer Unit - 100 Amp Switch with a 40 Amp 30mA RCD 2 Pole - Wylex, One 6 Amp Wylex MCB running Two 2ft 18w Non Corrosive Weatherproof Fluorescent Light Fittings and Two 20 Amp Wylex MCB's on the Two radial circuits.

I would greatly appreciate any feedback on this set up as, although i have been a mate for 4 years and done the course, i'm still wet behind the ears after having so much time off work and not being around the industry for a few months now.
Many thanks in advance
 
Not a good idea putting all 5 MCBs on the one RCD. Daz
 
You'll need what they call, a ''High Integrity'' CU where at least one of the MCB's will be unprotected by either of the RCD's. Either that or an all RCBO CU, where the supply out to the workshop will be protected by an MCB.


I take it you will be using an appropriately sized SWA buried cable for this new workshop supply??
 
  • Like
Reactions: 1 person
BG 13 way hi-integrity CU was £60 from screwfix. not metal box though. why you want metal box?
 
I take it you will be using an appropriately sized SWA buried cable for this new workshop supply??

the cable will be run along the wall of the house, across the top of a fixed gate and along the wall of the garage to the new workshop, all clipped and out of the way of any traffic.
 
was only going with metal for ease of termination of the swa gland ?

You can use a metal adaptable box to terminate the SWA cable, mounted directly under the new CU, and take the SWA cable tails through into the plastic CU...
 
  • Like
Reactions: 1 person
just need to verify the connections to the gas and water then.
 
i suppose i have to go get myself a Torque Setting VDE Screwdriver as well now too, seeing as its my test piece?
there was a lot of talk about them in the centre and i know there is mixed reviews as to the need for them
 
waste of space.
 
10 Way Hi Integrity Dual RCD + 100A Main Switch Consumer Unit

would i be better going for something like this then for the house CU?
with a 40 amp rcbo for run out to workshop?

The reason you are going for a High Integrity CU, is that you have an unprotected way (MCB) at the house CU. Otherwise you're not going to have any discrimination between the RCD device in the workshop CU and the RCD in the house CU!!! The SWA sub-main does not require RCD protection.....
 
  • Like
Reactions: 1 person
The reason you are going for a High Integrity CU, is that you have an unprotected way (MCB) at the house CU. Otherwise you're not going to have any discrimination between the RCD device in the workshop CU and the RCD in the house CU!!! The SWA sub-main does not require RCD protection.....

Noted...
im gonna shoot down the wholesalers in a min to have a look at their boards anyway as theres no exploded views on any of the web pages.
I was always going for an unprotected mcb, just had the wrong type of cu in my first list
 
Noted...
im gonna shoot down the wholesalers in a min to have a look at their boards anyway as theres no exploded views on any of the web pages.
I was always going for an unprotected mcb, just had the wrong type of cu in my first list

Just so long as you ''Don't'' replace the unprotected MCB with a RCBO!! lol!!
 
  • Like
Reactions: 1 person
Fitted out the shed today, came across a small problem "I think"?
i have bought the WYNH506, 5 Way Metal Consumer Unit - 100 Amp Switch from TLC and need to know if I can put the 40amp RCD in it? I will need to cut the bar down to size and obviously wire it up to suit, it's only that, all the pictures and boards I have seen that have RCD in have more than the one neutral bar. Can instill fit the RCD in or do I need to swallow the cost and start again with the install with a new board???
it will be a pain as I have already installed all the conduit, sockets and lights.
Just as you think you've had a good day too lol.
 
Fitted out the shed today, came across a small problem "I think"?
i have bought the WYNH506, 5 Way Metal Consumer Unit - 100 Amp Switch from TLC and need to know if I can put the 40amp RCD in it? I will need to cut the bar down to size and obviously wire it up to suit, it's only that, all the pictures and boards I have seen that have RCD in have more than the one neutral bar. Can instill fit the RCD in or do I need to swallow the cost and start again with the install with a new board???
it will be a pain as I have already installed all the conduit, sockets and lights.
Just as you think you've had a good day too lol.

Why didn't you consider the RCD before you bought the CU? What is at the other end of the supply to the shed?
 
I listed what I was putting in at the start of the thread and changed the house CU accordingly but didn't get any feedback about the 5 way board so thought it was ok. Learning about the boards is all trial and error and comes with experience as they don't tell you anything at all on any of the courses.
It all fits in the board (main switch, rcd, 2 20'sand a 6) it's just wether or not it can be wired up or not?
 
I listed what I was putting in at the start of the thread and changed the house CU accordingly but didn't get any feedback about the 5 way board so thought it was ok. Learning about the boards is all trial and error and comes with experience as they don't tell you anything at all on any of the courses.
It all fits in the board (main switch, rcd, 2 20'sand a 6) it's just wether or not it can be wired up or not?

So the house board has a single RCD?
 
Just replace the main switch with the RCD and plan ahead for future work.
 
So what's everyone got against metal consumer units? Different situations requires different solutions. An insulated board may or may not be preferable, it just depends on the circumstances.
 
So what's everyone got against metal consumer units? Different situations requires different solutions. An insulated board may or may not be preferable, it just depends on the circumstances.

I don't think everyone is against metal consumer units. Someone just asked why he was going for a metal one I think. Daz
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
New insall in workshop and CU change in house advice
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
PHS,
Last reply from
Guitarist,
Replies
34
Views
5,089

Advert