An alternative, depending on the cable runs involved, would be to put three DP contactors next to the DB, one per heater, each fed from an SP MCB and feeding the heater connection unit. Fit one stat in each room wired back in 1.0mm² to the contactor box. Feed the timer from a 6A control MCB either in the board or the contactor box, then take its output to both stats and the returns from the stat to the appropriate contactors. Advantages include not switching the heater load with the stats so they should last longer, and simplicity; three identical single-phase power circuits and one single-phase control circuit.
This I like, thank you for taking the time to think about it.

I agree yours is a more elegant system, but I wanted to avoid the complication and possible future confusion of feeding stat control lines back to the DB area. The runs are not easy.

I certainly agree about causing the stats to last longer - I like using relays for all kinds of things, and personally never use 13A stats direct wired on anything over about 6A, which this is, just!

I was using a 3P MCB only because there's a 4-pole contactor, and I like reducing component count. The 10A 3P MCB would simply be labelled 'Heating'.

Bloody hell this is a difficult call :) and I need to order parts and finish it by Thursday.

Here's a compromise I alluded to earlier: Keep the 3P MCB and one timer-circuit-controlled 4-pole contactor, which can be inside the DB so no external box is needed. Feed to three quality 13A stats, direct wired to the 6A heaters.

Do you think that under-run electronic stats with internal encapsulated relays are any less reliable than contactors? I agree that the old bi-metal type are trash, run hot and burn out, but those days are over. Aren't they? :-)
 
Last edited:
For completeness, here's what I did in the end.
TP breaker to 3-pole contactor in DB, controlled by local timer.
Switched L1 L2 L3 out to three separate wall-mounted thermostats, then onward to three separate heaters.
Not the most electrically elegant solution, but very simple, and consistent for all heaters so easy to understand in the future.
DSC_0730.JPG


DSC_0727.JPG
 
For completeness, here's what I did in the end.
TP breaker to 3-pole contactor in DB, controlled by local timer.
Switched L1 L2 L3 out to three separate wall-mounted thermostats, then onward to three separate heaters.
Not the most electrically elegant solution, but very simple, and consistent for all heaters so easy to understand in the future.
View attachment 56128

View attachment 56129
I'd have used SP breakers... so any future problems with a particular circuit wouldn't affect the other two.
External box for the controls, too.
...and (not your fault) that gunge in the cable entry point is horrible and pure daft IMO.
 
I like how the vents in the top and bottom rear of the enclosure are sealed up too.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Mark42

Patron
~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Timer and local thermostat control of 3 x heaters on 3 phases. Wiring logic help please!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Mark42,
Last reply from
freddo,
Replies
24
Views
4,175

Advert