This makes no sense. The load is determined by what people plug in, not by how you wire the sockets. What makes even less sense is the total consumption. Think about the heat you get from 120A (almost all electrical power gets converted to heat before it leaves the room)
120 x 230 = 27.6kW. Unless they leave the hot taps running, turn the heaters to max, keep refilling the kettle and take seven extra fanheaters in there they are not going to use 120A. The people would overheat even if the cables don't. If the installed heaters are adequate, the RFCs are going to see a couple of amps total except when the kettle is on.
Also, 2kW lighting? You can't buy GLS lamps any more