Discuss Lighting with no CPC and installing new CU (Domestic) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
An RCD will make a (lighting) circuit without a cpc safer.
Obviously if all the fittings and accessories are plastic then the situation is not likely to occur, other than putting your fingers on the contacts.
Following this argument would mean that an RCD is of no use on an electric shower circuit as the shower is plastic.
However, should the homeowner fit a class one light fitting or switch on a circuit without a cpc and a fault occur causing it to become live then if touched the RCD will operate and disconnect the supply.
Therefore the circuit is safer because of the RCD.
RCDs do not rely on or use the cpc (other than N-cpc faults) to achieve their intended purpose and so the argument that they will not make a circuit without a cpc safer has no basis.
RCDs have the same result whether or not the circuit has a cpc (other than N-cpc faults).
are you for real ??
rcd must have an earth to operate .......... L-E FAULT rcd trips
N-E FAULT rcd trips
L-N FAULT rcd does not trip since this is short circuit
so how does an rcd make it safer without an earth??????
you cant say what if the customer does this etc in the future , what if the customer opens the consumer unit and licks the buzz bar
should we lock the consumer unit away ???
Ok here is a scenario that I have encountered a customer got a shock because he was putting the kettle on whilst switching the kitchen lights on what was found was that there was no earth at the switch and the shock he got was induced AC as the fault was fixed by reconnecting the earth but what if the switch box was live now in the same scenario would you prefer an RCD or not I dont think there is or should be a debate here because I know what level of protection I would want
L-E FAULT rcd trips
MCB would trip anyway but I thought we were talking about circuit without cpc.
N-E FAULT rcd trips
Agreed. I did say other than N-E but I thought we were talking about circuit without cpc.
MCB would trip anyway.
See above.
If they have done it in the past it will be safer with an RCD.
It will be safer (? less dangerous) with an RCD.
N-E FAULT rcd trips
Morph mate think about it, If you touch a live contact. I.e. lampholder pin, the current flows through you to earth, so regardless of having a CPC in the circuit and RCD will theoretically make it safer. RCD's act on imbalance of current between L and N, They don't care whether circuits have an earth,
If you touch a live contact stood on the bath on a NON-RCD protected circuit, 6A would need to flow through you to operate the MCB
If you touch a live contact stood on the bath on an RCD protected circuit, 30mA Would need to flow through you to earth (through the bath) to operate the RCD.
CPC in the circuit is irrelevent in this case. In fact I think the issue you are having is distinguishing between a circuits CPC and EARTHING.
Is it not the case that if you were to touch the live terminal, conductor etc, you would unless standing on a rubber mat provide a path to earth for the current to flow (hence a shock) so this would unbalance one side of the rcd or rcbo and cause it to trip ? If so this would be the case with or without an cpc in circuit.
Reply to Lighting with no CPC and installing new CU (Domestic) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net