Yes dead right! ^^^^
Discuss Lighting with no CPC and installing new CU (Domestic) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
rcd must have an earth to operate .......... L-E FAULT rcd trips
N-E FAULT rcd trips
L-N FAULT rcd does not trip since this is short circuit
so how does an rcd make it safer without an earth??????
you cant say what if the customer does this etc in the future , what if the customer opens the consumer unit and licks the buzz bar
should we lock the consumer unit away ???
For shock protection - their purpose - yes, they need an earth path,i.e. a person, not a cpc.
What will happen if you touch a live exposed conductive part which has no cpc but is protected by an RCD?
Morph mate think about it, If you touch a live contact. I.e. lampholder pin, the current flows through you to earth, so regardless of having a CPC in the circuit and RCD will theoretically make it safer. RCD's act on imbalance of current between L and N, They don't care whether circuits have an earth,
If you touch a live contact stood on the bath on a NON-RCD protected circuit, 6A would need to flow through you to operate the MCB
If you touch a live contact stood on the bath on an RCD protected circuit, 30mA Would need to flow through you to earth (through the bath) to operate the RCD.
CPC in the circuit is irrelevent in this case. In fact I think the issue you are having is distinguishing between a circuits CPC and EARTHING.