For the purposes of emergency lighting can anyone define borrowed lighting for me.
I have seen a number of different Fire Authorities guides and recommendations and these are some of the definitions of Borrowed Lighting I have found:
  1. light obtained from another nearby source of emergency lighting.
  2. Natural light eg moonlight.
  3. Street lighting.
I have done some lux meter readings on the fire route/outside staircase of a 4 storey block of flats.
1/4 moon 1/2 moon and full moon no problems.No moon the centre line is over 1 lux .
No moon and overcast sky part of the centre line drops to .8 lux caused by shadow from the iron girder supports.
This affects 5 x300mm sections of the route .
If I had not taken the readings on an overcast moonless night I would be none the wiser,so how can natural light eg moonlight be acceptable as borrowed light.
thanks
 
another defination says 'it is the light entering an interior and otherwise dark room or passage from an adjoining space having windows or skylights.'

so as long as the overcast /no moon night doesnt have any lux, its no longer viable to refer to it as borrowed light
 
Last edited by a moderator:
Guessing only


  1. light obtained from another nearby source of emergency lighting. Most likely this.
  2. Natural light eg moonlight. You can't guarantee this light being there.
  3. Street lighting. You can't guarantee this light being there either, if there is a local power failure.

 

Reply to Borrowed lighting definition required in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to wire up a small kitchen for a local charity. 1 x 32a cooker 4 x sockets fridge/Dishwasher Cooker Hood 2kW water heater It's...
Replies
14
Views
2K
Am I on the right lines, I ask? I've just recently moved into this house which is nicely equipped with a large 15 circuit CU unit with a split...
Replies
18
Views
3K
This might be long so feel free to grab a brew. So, as some of you may know, i'm a 34 year old who has been dying to get into the industry. I...
Replies
66
Views
9K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Any info would be greatly appreciated. I have just rewired a HMO and have now been asked to do fire alarm and emergency lighting. I have wired...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock