They did ramp tests of everything. They did various Zs tests. They discovered I have 1V between earth and neutral and pondered that for a while. They tried disconnecting things. They changed out the RCBO and then back again. The last one was just about to do insulation resistance tests - but ran out of time. If I can't find anything, then that will be the next thing - but I'll get him back to do that.
Have ordered the meter and will do measurements. However - have done the following experiment FYI:
in the property which does NOT fail. Completely empty ring main. 30mA RCD (blows around 23mA). Runs pump just fine.
I added my resistance box and loaded up 21mA of additional earth leakage before the RCD blew.
Seems to me to confirm that the pump itself doesn't have more than a few mA of leakage.
Also talked to the pump manufacturer. Apparently it is a soft start inverter. It has a start-up current of about 1.5x for a few hundred mS. It is rated at 0.9kW.
Have ordered the meter and will do measurements. However - have done the following experiment FYI:
in the property which does NOT fail. Completely empty ring main. 30mA RCD (blows around 23mA). Runs pump just fine.
I added my resistance box and loaded up 21mA of additional earth leakage before the RCD blew.
Seems to me to confirm that the pump itself doesn't have more than a few mA of leakage.
Also talked to the pump manufacturer. Apparently it is a soft start inverter. It has a start-up current of about 1.5x for a few hundred mS. It is rated at 0.9kW.