B1gSte

Hi everyone. Could someone please explain how an LED bathroom mirror with shaver socket should be connected to the mains?
My interpretation of the regs is that a fused spur must be outside the zones.
However, can the flex be connected in the void behind the mirror and by what means?
I am not making the connection myself. This is part of an extension build (en suite) and I’m just trying to make sure that everything is in the wall ready before the boards go over the studwork.
Any advice appreciated. Thanks.
 
if it comes from the lighting circuit, no FCU required. cable direct from lighting in attic to connect to mirror flex or terminals.
 
Thanks for your quick replies. So to verify. No FCU required.

Nebu1a, so to verify. Is the connection plate permitted behind the mirror above the basin?

Edit: Does cable need to be run in conduit?

Thanks
 
Thanks Wilko there is a B6 switch for both the upstairs and downstairs lighting circuits at the CU. Is that what you refer to?
 
How close is the mirror to the shower or bath?

Also as the flex outlet plate is behind the mirror, which I am assuming needs tools to remove, it could be argued that the flex outlet plate is out of zones anyway.

It is standard practice to fit illuminated mirrors on the lighting circuit. Do the MIs state it needs to be on a fused spur?
 
Is there a switch labelled as RCD?
Bathroom circuits need additional protection by a 30mA RCD.
 
I don't get why the customer needs to check for wiring provisions and RCD protection.
When I do a bathroom fit the customer tells me they are having a mirror and I do all that myself.
 
  • Funny
  • Agree
Reactions: Midwest and 123
The existing CU has only a 63A 30mA RCCB on the kitchen and house ring mains.
The other side of the CU has a load of miniature circuit breaker type switches that stats NOT protected by RCCB.

However, I already have an electrician on standby to replace the whole CU as the meter box has been relocated to outside. So the present set up is temporary.

So on the assumption that he will replace to present standards, I just need to know what connection to use behind the mirror.

In answer to question above, the mirror can be lifted off the bracket without tools.
The basin unit with mirror above is next to the shower screen. Shower is 800 x 1200. Centre of sink is 400mm from shower screen.
 
Andy78. The boards are going up shortly I just need to make sure I have made provision for the electrician when I get him round to do all the rest of the extension including kitchen and new CU. Thanks.
 
Last edited by a moderator:
400mm puts the mirror within zone 2.
You will need to ensure the mirror is suitable to be used within zone 2.
 
What about if I put a conduit in the wall with a piece of string through from above so that the electrician can pull a cable (or the long flex of the mirror) through it later?
 
  • Like
Reactions: Flanders
Fit noggin, 25mm metal back box, conduit and draw wire and leave for your electrician to finish. Check the mirror is suitable for Zone 2.
 
  • Like
Reactions: B1gSte
Thanks Nebu1a that’ll do for me!
The mirror is one of those Hudson Reed LED things with a swipe sensor switch for the lights, a shave socket and a demister pad. It is shown above a sink in all the marketing ads. I know this doesn’t necessarily mean anything. It says IP44 on the back, which i have read (on here I think IIRC) is suitable for zone 2.

Thanks again.
 
I'd just leave the cable hanging (not energised of course) out of the wall. Then when you, sorry your electrician comes to test - inspect - connect wall cabinet/mirror, it'll go straight inside the fitting.

However, if its one of those luminaires that comes with a pre-installed flex, which is difficult to remove, I'd go with one of those aforementioned alternatives.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Connection behind bathroom mirror?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
B1gSte,
Last reply from
Tim Court,
Replies
33
Views
32,261

Advert