Hi, I have installed a Danlers occupancy PIR in a bathroom. This operates two 4.5watt LED bulbs contained in the obvious downlight housings and a Icon low voltage fan. When the PIR timer runs out the fan carries on running indefinitely. There remains around 50volts at the fan transformer. I have been informed by Danlers that I need to install a "Resload E ". Has anyone else come acroos this problem or similar?
 
Hello Flying Penguin, welcome aboard. Enjoy the forum. :D
 
Hi & welcome. :)

Normally with a danlers PIR they recommend a capload. The resload is normally with trailing edge dimmers.
 