hutch6447
Hi all ran supply to outdoor garage as this is being assessed just want to double check.
Main consumer Board 32 amp RCBO ran on 4mm SWA to the garage then onto the garage consumer unit.
Ran overhead but less then 3 metres length between house and entry point at garage, so just ran it direct.
Running into the garage consumer got the SWA on a banjo connection then going on to power the 30mA rcd.
MCB's in garage are 1 x 20A 1 x 6A
Plug sockets Radial ran on 2.5/1.5
Lights ran on Radial 1.5/1.0
Ran all test's and they were well inside limits BS 7671