Filling out the above for a Sub board (D.B 12)

TN-S
TP&N

There is no board fed from abnother board, there all split in henleys straight from the meter.

D.B 12 is single phase.

Im getting Zs of circuit 1 as 0.22
R1+R2 as 0.06

Previous PIR's show Ze as 0.22 but how can this be if a circuit Zs is 0.22??
I cant isolate the entire building to obtain a true Ze reading.

PEFC at D.B 12 shows up a Ze of 0.19, obviously this is not a true Ze due to the amount of earth paths.

Just abit baffled on filling this one out for this D.B 12

Or maybe its getting late and im just being dumb!!
 
Just record your measurements.

If you cannot record Ze then record it as so.
 
maybe spark who did previous PIRs was an idiot!!?? / under pressure to do PIR in 10 mins!
 
0.22 could be the actual Ze, don't forget that parallel earth paths through the water and gas services can improve the overall loop reading especially if the incoming services are in lead or steel pipe and you're close to the substation.

Also you don't know the comparative accuracy of your test meter and the previous guys meter. Considering the tolerances can be as much as 5% on some calibration certificates the readings could be accounted for.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
filling out certificate
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
TPES,
Last reply from
Dunc,
Replies
3
Views
1,690

Advert