Thread conclusion!
The customer at last agreed to the fault finding on the high Zs results.
I returned today, the customer told me his son had opened up the conservatory sockets and may have fixed the problem!! I tested the Zs, it was now 12Ω rather than 4Ω
I opened the socket that I thought was were they had extended the ring and found 3 earths loosely connected together and one earth not connected at all. Connected it all up properly and the Zs is now 1.06Ω. (Still close to the 1.1Ω max Zs for a 32A Type B MCB, those max figures are coming down aren't they!)
A happy customer as he thought I was going to be there much longer, as did I!