dickiegeorge

Today my sister moved into a brand new 3 bed property. I looked at the distribution board and found that it had one ring main serving the kitchen, GF and 1st floor protected by a 32 amp mcb and a 80A 30mA RCD. I know that you can theoretically have unlimited sockets on a circuit but is this acceptable design? Does it conform with regs? It serves 25 points in the house
 
Appalling, I always have 4 rings, up, down, kitchen general use, and kitchen appliances, but thats me, over the top maybe.
 
  • Like
Reactions: 5 people
No it doesn't meet current regs, no segregation of circuits. Needs to be at least one up and one down. Any good spark would do that plus put the kitchen on its own.
 
  • Like
Reactions: 2 people
Bad, bad, bad. Are you saying there is one up front RCD protecting ALL the circuits?
 
I believe it's really bad practice but I can not think of any Reg to say it is against that. But it is against Approved Document P I think.
 
typical rush rush rush dont give a stuff as long as it works and we get paid just no design thoughts ,just done a referb 3 bed bungalow its got 4 ring mains 4 lighting circuits ,freezer supply boiler supply ,and it has a run of cable tray running from one end to the other for the main loom and not one area does it cross the beams
 
If you look carefully outside you can probably see where the installers horse stood! Usually go for 3-4 ring finals on our jobs
 
I've heard a few lads noticing this in new builds lately. Seems to becoming common.

fuffin better not be. I'm in the middle of buying a new build. if I find out its like that I'll be ripping the place to ****ing pieces
 
Thanks for everyone's replys. It's a split board, one RCD covering 4 mcb's which are lights up, lights down, heating and cooker. Other RCD for the one mcb protected ring main. I'll advise her to talk to the builders about it but is it too late?
 
Thanks for everyone's replys. It's a split board, one RCD covering 4 mcb's which are lights up, lights down, heating and cooker. Other RCD for the one mcb protected ring main. I'll advise her to talk to the builders about it but is it too late?

Too late, probably. Builder guilty of cost cutting - 100%
 
Thanks for everyone's replys. It's a split board, one RCD covering 4 mcb's which are lights up, lights down, heating and cooker. Other RCD for the one mcb protected ring main. I'll advise her to talk to the builders about it but is it too late?

^^^^^^ can someone post up the reg numbers about this statement, just so wrong. I would do it myself but I no longer have the patience
 
all lights on one mcb, one ring main WTF are they thinking and how are they still working lol
 
Thanks for everyone's replys. It's a split board, one RCD covering 4 mcb's which are lights up, lights down, heating and cooker. Other RCD for the one mcb protected ring main. I'll advise her to talk to the builders about it but is it too late?

I'd say definitley too late...he'll be back in eastern europe somewhere by now :38:
 
  • Like
Reactions: 1 person
A ring circuit is allowed to cover an area not exceeding 100m square.

What's your floor area where this circuit covers?
 
A ring circuit is allowed to cover an area not exceeding 100m square.

What's your floor area where this circuit covers?

That's not strictly true any more, it's a historic guideline. Still a guideline today, though. I'd say the biggest issues are potential overloading of the ring circuit, lack of circuit segregation and possibly circuit length.
 
That's not strictly true any more, it's a historic guideline. Still a guideline today, though. I'd say the biggest issues are potential overloading of the ring circuit, lack of circuit segregation and possibly circuit length.

Plus nuisance tripping by accumulative build up of earth leakage
 
  • Like
Reactions: 2 people
I think what your all missing here, is that if this new build is part of a development companies estate, then the electrician(s) would be following an approved drawing and specification drawn up by either the development companies electrical Engineer, or the companies Architect!!

This all smells to me, like a cost cutting exercise by the actual developer using the Reg's to it's minimum requirements, rather than it being down to the electrician that installed the installation!!
 
  • Like
Reactions: 4 people
Yes it's a new estate built by David Wilson Homes. I can't imagine a buildings inspector would accept work like this if it was was carried out on a rewire. Or maybe he would?
 
Yes it's a new estate built by David Wilson Homes. I can't imagine a buildings inspector would accept work like this if it was was carried out on a rewire. Or maybe he would?


So what would you expect a Building Inspector to know about electrical installations?? These housing development sites are almost totally controlled by the developer themselves, and as i said, they will be working to ''approved working drawings'' and to a ''specification'' which were probably accepted by the local council LABC/Planning dept, prior to anything being built!!
 
majority probably 99% new builds you get a plan of the building,showing electrical services, you count it off and design yourself. The 10yr man inspects might snag for more clips, but he does not go the CU and count circuits. Then once signed off all he asks for is a copy of the cert, and demo of smokes etc and then hes happy. They never dabble to deep into the electrical side.

Ps the last inspector pulled me for not writing spare on the spares,and the lad doing the next house didnt put a label on the cu stateing next test date (as it read on snag sheet-no red label- being the niceic printed ones he was referring to lmao)
 
I'm interested in peoples fascination with ring final circuits? I haven't wired a ring for years! Radials every time for me :)
 
  • Like
Reactions: 2 people
I'm interested in peoples fascination with ring final circuits? I haven't wired a ring for years! Radials every time for me :)

Noooo! Don't start that debate again......mind you I can't resist. :)

I think rings and radials both have their place but I install more and more radials these days. Some sparks I think still automatically think sockets = ring. I still install a ring for kitchens, but often radials for living room, bedrooms etc. Problem is, in my view there is no decent alternative to a 32 amp ring. A 32 amp radial wired in 4mm is limited in terms of installation method. You're pretty much limited to ref method C cos the CCC of 4mm drops below 32 amps pretty quickly! Not to mention the 1.5mm CPC limits circuit length.
 
  • Like
Reactions: 1 person
Noooo! Don't start that debate again......mind you I can't resist. :)

I think rings and radials both have their place but I install more and more radials these days. Some sparks I think still automatically think sockets = ring. I still install a ring for kitchens, but often radials for living room, bedrooms etc. Problem is, in my view there is no decent alternative to a 32 amp ring. A 32 amp radial wired in 4mm is limited in terms of installation method. You're pretty much limited to ref method C cos the CCC of 4mm drops below 32 amps pretty quickly!

If you exclude kitchen/utility areas what realistically do you expect the "load" to be in the average house for a ring/radial - not much.
 
Problem is, in my view there is no decent alternative to a 32 amp ring.

Two 20A radials :)

Each to their own I suppose, I'm not trying to start this debate again, like you said I just find most sparks fascination with rings (no pun intended) rather funny :D

We work domestic, commercial and industrial and it has been a very long time since we last designed to accomodate a ring final circuit!
 
  • Like
Reactions: 1 person
I'd rather see four radials ove a couple of staggered RFCs :D
 
  • Like
Reactions: 1 person
Nothing wrong with radials IMO, but I would certainely have the kitchen on a ring, or 2 haha, JMO, anyhow however back to the original OP, one ring for the whole house is pretty shocking really, the building inspector must be taken to breakfast regulary to decide not to look at the board and let that go.
 
Nothing wrong with radials IMO, but I would certainely have the kitchen on a ring, or 2 haha, JMO, anyhow however back to the original OP, one ring for the whole house is pretty shocking really, the building inspector must be taken to breakfast regulary to decide not to look at the board and let that go.

He can't really say anything can he, even if he did know what he was looking at, ....if they have approved working drawings based on accepted drawings from his own council planning dept!! lol!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
One ring main covering a brand new 3 bed house
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
65

Advert

Thread statistics

Created
dickiegeorge,
Last reply from
Stroppy,
Replies
65
Views
18,895

Advert