Have come accross a job where house ring run in T/E but has an old extension with earthed metal conduit used for sockets and only live and neutral single cores (of which are both black here).
The earth continuity is greater than 500 ohms and the live is faulty between 2 sockets and disconnected.
For now I have down rated mcb to 16A and looking at rewiring the sockets with the conduit wiring.
My issue is that it is a solid floor covered with laminate, a flat roof and internal walls are stone with current metal conduit and boxes fitted during build within the stone work.
Would it be acceptable to rewire the sockets using SWA on the outside of the building to replace this part of the ring (5 sockets in total to rewire on a final circuit of 18)
Any other ideas/advice appreciated as cannot seem to find any other way.
 
I can’t see a problem with what you intend to do if you are in the uk.
local regulations may prohibit it though and you don’t mention where in the world this is.
 
  • Like
Reactions: pc1966 and sidekick
I can’t see a problem with what you intend to do if you are in the uk.
local regulations may prohibit it though and you don’t mention where in the world this is.
Thanks. Ilkley, west yorks
 
I can’t see a problem with what you intend to do if you are in the uk.
local regulations may prohibit it though and you don’t mention where in the world this is.
Thanks. Ilkley, west yorks
 
Can you pull the existing wires through the conduit and pull in new ones along with a CPC to link all ends of the conduit/accessories?

If not then the suggestion of NYY-J outside makes sense.
 
  • Like
Reactions: Julie.
Can you pull the existing wires through the conduit and pull in new ones along with a CPC to link all ends of the conduit/accessories?

If not then the suggestion of NYY-J outside makes sense.
Agree, why not pull new main cores and CPC using the old.

If its a concreted in run, the installer usually plans the run suitable for a new pull through (though not allways)
 
  • Like
Reactions: James

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
.
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
.
Business Name
.

Thread Information

Title
Running SWA on outside of building to feed part of internal ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
sidekick,
Last reply from
Julie.,
Replies
6
Views
1,363

Advert