can any one advise does the armouring on swa cable on dc side does it need earthing also does cable tray on dc side need earthing and what about containment on a roof is that left floating getting told different answers of different people people.and 1 more thing is there some kind of single flex to connect between inverters and isolators that goes up to 10mm. any one
 
Is the inverter transformer-less or not?

If the inverter has a transformer then you don't need to earth anything on the DC side.

If the inverter does not have a transfomer then...

Rule of thumb CPC half of line conductor but as it's outside minimum 4mm
Bond the mounting (all significant rails) together.
Bond the armour of the SWA together with the frame to a new TT earth electrode
Do not bond the SWA armour to the earth terminal on the inverter as this is (normally) within the equipetential zone of the property.
All the outside gear bonded together and taken to the new earth electrode.
Test new earth to AC line as normal to determine Ze of new electrode normal rules apply <100ohms (200ohms permitted)

That's how I understand it, anyone got any different ideas?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
solar p.v earthing
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Phantasmagoric,
Last reply from
Ramjam,
Replies
1
Views
3,355

Advert