An underground tt supply going into a meter cabinet on the outside of a garage, 16mm tails straight through the wall to henley blocks, 10mm earthing conductor to a rod with a Ze of 38ohms. From henley blocks a small gagage sub main with a 63A 100ma T rcd, main house feed from henley blocks (in 16/16/16 split concentric cable) back into the meter cabinet and through underground ducting feeding house cu where circuits are protected by 2 x 80A 40mA. House built approx 1980.
Asked about this at school yesterday where I was lent gn8. From my reading there could be two issues.
1) Lack of a 100mA T rcd protecting the house feed and
2) The house feed needs a cpc but this should not be connected (house cu end), instead a separate earth electrode should be provided.
So my confusion is that the logical, practical and most convenient place for this new rod is back through the ducting to roughly where the existing rod is but only in 10mm. Surely it makes sense to keep the existing 16mm earth rather than replace it with a 10mm one.
Am I misreading something? Don't worry, I am not the person doing this, just trying to learn!
 
If the house CU is more than 3 meters away from the main fuse then there needs to be an overcurrent protection as well as an RCD. Also the 1st enclosure (where the RCD is) should not be metal - class II.

Can't see a problem with the earth to the house CU if I understand what you're saying.
 
Heley blocks to 80A fused isolator and then split con to house. The garage rcd only protects the garage submain.
Gn8 clearly shows the cpc running alongside the feed but not connected at the house end but a separate electrode being used. Two different equipotential zones I assumed
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

mhar

Arms
~
Joined
Location
devon

Thread Information

Title
Think I must be confused!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
mhar,
Last reply from
mhar,
Replies
2
Views
1,398

Advert