Good morning guys and girls
I have attended a kitchen rewire this morning to test a install buy a 3rd party.
The boiler spur is directly above the draining board I'm quite sure this shouldn't be the case. I've been told by the installer that "it's fine it's rcd protected" is this just waffle to get me to sign it off.
Surely it's the same principle as a light switch inside a bathroom?
 
If you are signing off a third party cert, were you not involved at the start of the job ?
There is nothing to say that a FCU cannot be near a draining board, just as there is nothing wrong with a plate switch in a bathroom.

Suitability for the environmental effects likely to be encountered is the reg you have to consider here, and that's your call.
 
If you are signing off a third party cert, were you not involved at the start of the job ?
There is nothing to say that a FCU cannot be near a draining board, just as there is nothing wrong with a plate switch in a bathroom.

Suitability for the environmental effects likely to be encountered is the reg you have to consider here, and that's your call.
The work was done by the kitchen fitters my boss has just sent me to do a test on the whole house.
I personally wouldn't put the spur that close
 
The work was done by the kitchen fitters my boss has just sent me to do a test on the whole house.
I personally wouldn't put the spur that close

Which scheme are you notifying the work through ?
The 2 schemes that I know of that offer third party notification, Napit and Stroma, both require inspection at first and second fix.

You will be signing your name to the fact that you have inspected the cables at first fix and that all is compliant. If you personally are not happy with how things have been done, then don't sign your name to it.
 
Does seem odd, if he's doing an EICR then he shouldn't be concerned about one specific issue, just give an honest appraisal of the whole installation. If he's doing a MWEIC or EIC then he can't be recommending improvements!!
From what I can gather the landlord has asked us for a EICR and has had a new kitchen fitted and new services
 
One of the first thing you should ask for when doing a periodic inspection is previous certs, especially recent ones. Ask for the certs, make a note on the report if there are none to the effect that recent work has not been carried out to BS7671, code the FCU referencing specific regulations if you see fit, job done.
 
Good morning guys and girls
I have attended a kitchen rewire this morning to test a install buy a 3rd party.
The boiler spur is directly above the draining board I'm quite sure this shouldn't be the case. I've been told by the installer that "it's fine it's rcd protected" is this just waffle to get me to sign it off.
Surely it's the same principle as a light switch inside a bathroom?
Lets put a double socket over the bath to plug the fire in well its RCD protected it's fine !!!!!!!!!
 
I take 300mm as a basic rule as above as no direct reg stating distance,regarding testing if I have read the posts correctly you work for a NICEIC D.I. firm.NIC don't do 3rd party, kitchen fitters do work you test it as condition report and your company notifiys it as they done work to building control via NICEIC web site this as well as the cert being forged as satisfactory this is not correct.
 

Reply to Boiler spur location in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock