Discuss New supply from transformer mast for 9 separate metres property connections? in the Commercial Electrical Advice area at ElectriciansForums.net
R
Richard Knight
Hello,
We purchased a plot of land a while ago and we are trying to establish how we can actually connect into the mains transformer mast which is available on site.
Originally we had 3 options. There was a Scottish power owned cable that we could tap into this would cost £4500.00 to link to just our plot as it would be over 150m distance. Or each plot owner could take their own supply from the mast and have a single 100amp connection which would be metered and then extended using the private cable laid which links it to our plot £1200.00.
Or all the plot owners could chip in together on a communal solution - distribution fuse board?
Scottish power have said that if everyone does one of the first two options then there wouldn't be enough capacity on the transformer mast to supply everyone... So we have asked them to price for the distribution fuse board.
This is what they are pricing for:
We shall install and connect a 400v low voltage three phase cable from the LV pole, install a 9 way DFB, install 9 x 2m x 25mm LSOH cables from DFB to new cut outs, reconnect and energise the existing meter to one of the new cutouts. Our works will include 22m of service cable. All excavation, backfill and reinstatement will be carried out by the customer.
When I spoke to them on the phone they told be that this will give 9 x 60 amp connections (all separately metered) 100 amp cable head into the DFB, the DFB is protected by an 80 amp fuse and then each cutout of the DFB is protected by a 60 amp fuse...
I want to check that that means that all 9 properties can draw of 60 amps at the same time?
They have priced £4500.00 inc VAT for the works, seems quite a lot but I guess these things do cost allot! £458.00 of work is non contestable but the rest could be done by an approved company of a list they gave us... Do people think it's a fair price or should I try and get some further quotes?
Any advice is greatly appreciated!
The chances of all the properties trying to draw 60amps at the same time is about the same chance of winning 1st prize on the Lottery.
Scottish Power are in the distribution business, they'll know that what they are providing will do the job. If it doesn't they'll have to upgrade it at their own expense.
The worst load case would be 3 x 60amp from 1 x 80 amp fuse.
£4.5k is cheap for 9 properties, it can cost £15 to £20k for a single new remote connection
The price sounds good even by my local African standards, I'd accept before they change their minds.
A 60A connection per dwelling should be more than adequate and if they're offering 9 connections then they'll have done the diversity calculations and they'll be happy they can provide sufficient power.
Is your plot the most central for all 9 DNO supplies to be taken from and what sort of distance is it from the existing DNO supply?? What sort of distances are we talking about from this central panel, (let's call it a Ryefield panel) to the other plots??
The Ryefield (DFB) board to be protected by an 80A fuse. So that three plots on each phase fused at 60A. Not much by way of discrimination.
What do you think?
The transformer mast is about 4m from the communal metre hut which will house the DFB.
Our plot is the furthest away from the DFB Arround 150m to the consumer box point int the house.
I can upload a site plan showing locations, would that help?
i just want to feel comfortable with the proposed solution, as it's all been very stressfull!
Thanks for the help everyone!
There's one vital bit of information missing.
Are the properties all 5 bedrooms with plans to have swimming pools, saunas etc?
Has anyone done the calcs and costing for the 150mtr cable to your house, the cost of that is going to far exceed the DNO costs for that house.
Hi Snowhead,
Our property is 3 bedrooms and two bathrooms. Low energy everything! Heating is LPG. 60 amps should be plenty considering the planning restrictions. They are Holliday chalets in woodland setting.
Our assumption is that we will run a 25mm 3 core armoured cable from the DFB, roughly 150 metres. I believe this will accommodate 60 amps, this will of course be designed and installed by an electrical engineer we have in mind.
I'm sure the electrical engineer would tell us if 25mm isn't suitable, I'm not sure on our max load at the moment. Say it was 60 amps... What would be suitable given the distance?
thanks!
thanks!
If it was 60 amps, alot more than 25mm. To limit your VD to roughly 3V, you'd need 150mm conductors. To keep your VD below 3V you're looking at 185mm conductors.
Christ sounds expensive. From initial discussion with the electrical engineer he intimated that 25mm would be suitable with a sensible house usage design. We will see I guess :/ . Funny thing is the land owner laid 10mm cable to connect all the properties, we naively didn't see this as a problem when we bought the plot! Lesson learned, hard lesson!
To comply with the volt drop requirements at 150m then you would need to be limited to 25A to use 25mm² SWA.
It may be that the electrician designed this with an anticipated diversity for each property to that the expected (average) current would be 25A or less.
The 10mm would have been installed only considering current carrying capacity not voltage drop.
I still think 25mm is too small for 150m. I'd certainly consider checking the credentials of this so called 'engineer' as for a 25mm cable to be suitable, and to keep your VD down to roughly 3V your max demand would have to be under 10-11A, highly unlikely for a house.
Wrong forum, but have you got the costs for New Water supplies?
And Foul drainage connections or is it Biodigestor?
We paid £3000.00 to the development site owner, this was to lay down and connect us into the mains water supply and the electrical mast available on site.
Can of worms... The water supply had issues, there wasn't enough pressure to supply the lodge plots at peek demand times. This has been rectified for other plot owners using a large break tank and pumps... we didn't buy into the system. The development owner wanted another £1200.00 for this. So we have decided to have our own holding tank in the property.
We bought the plot with SEPA consulted and agreed systems...
The system we are going for is a domestic sewage treatment plant, this removes 95% of bacteria where as a septic tank removes just 10% (if I remember correctly those figures are accurate)
All plots have passed percolation tests, apart from ours - the day ours was done the area got record rainfall so was't a fair test. The development owner has paid for all test for other plots... but he is refusing to pay for our re-test. Looks like that will be another £1200.00 for a SEPA consultant to test it and design the system.
Self-building is bloody expensive and stressful! But also very exciting, I hope it's worth it in the end!
All of which is WHY i asked about the distances involved questions above!! ...lol!!
The other question that should be asked, is how are you (OP) intending to run these supply cables to each plot?? Without knowing the layout, the distances may well need to be in excess of what your planning. Eg, are these cable routes following paths/road or as the crow fly's, crossing the other plots underground?? If the latter, you may need to go deeper than the recommended 600mm (60cm) and be run in heavy duty ducting....
I'm not laying any cable for anyone else... just our own plot.
There is a 10mm cable laid in at the moment, which isn't of any use to us - maybe a temporary supply for plugging in tools - that would be useful and save on petrol with the generator! Max load would be 25 amps as suggested by the engineer and calculations above.
Not crossing any plots, following the road. It has been measured countless times. 115m to the edge of the plot, then another 30m to the entry point in the dwelling.
Here is the cable calculation for 10mm cable at 150m - he intimated it would give 25 amps at 5% VD.
The above doesn't make much sense to me.
I don't know much about his design software, but if that's what he's saying then he's wrong I'm afraid, very wrong!
On a 10mm three core thermosetting SWA, 25A over 150m results in a voltage drop of 17.6V, or 7.6%, 2.6% over the maximum allowed for general circuits according to the guidance given in appendix 4 of BS 7671.
Thank you for bringing this to our attention!
Having looked closer at that picture, I've so far counted what appear to be at least 9 glaring errors with the software?!
Is anyone else in a position to confirm or dispute?
Is this a wind up? It was Friday yesterday.
For someone to buy a plot of land with such obvious problems beggars belief.
As for this being a self-build, it has all the hallmarks of a disaster epic. Lots of money sinking without trace.
No wind up... what's Friday got to do with it, have no idea what your'e talking about! When my parents bought the land they were naive! They put trust in a NHBC housing developer (who is selling the plots) and the solicitors who dealt with paperwork. Lesson learnt for them, they wont make that mistake again if they buy development land in the future.
I will be glad when the services are sorted, everything else is fully in our control regarding building works. My parents have experience of multi-million pounds worth of building projects.
Given the problems with the electricity, water and sewage I would suggest you employ a project manager that knows what he is doing.
Your comment “I’m not running cables for others” is incredibly short sighted. As for your plot having its own potable water and sewage arrangement is bordering on stupidity.
You would seem to have alienated yourself from the other owners and now you’re going to pay for it.
But as it’s your money, do as you will.
I assume you are paying this supposed “engineer” for his services, I find it somewhat offensive that you come here expecting total strangers to assist for nothing.
Water is sorted, we have an individual holding tank that will serve our property if pressure does drop during peak times.
Electricity... well Scottish Power Energy Networks have designed the system, think they know what they are doing...
And we are employing a SEPA drainage expert for the percolation test and drainage reports who will design a suitable system.
Don't think we need a project manager to do that mate, as it's all sorted and in the pipeline.
Why would I run cables for everyone... I'm not the original land developer, I have liaised with SP to identify a possible solution for connecting into the mains electric for everyone. Pretty sure everyone is happy I have done this for people. They aren't expecting me to lay and connect cable to there plots, I have no idea why you think I would do that.
Say you live on a normal street and everyones gates get stolen, are you going to go out and buy and fit everyone new gates... fair play if you are you must be a very generous and kind person...
We are not alienated with any plot owners, some are good friends some I have only met once as we haven't been on the site full time yet. The only person that we are alienated with is the original land developer, who in my opinion hasn't done fully what I expected from him. But life is to short to start a legal battle with him or fall out majorly... he will be one of our neighbours when he gets his lodge built so it's just not worth it!
"I find it somewhat offensive that you come here expecting total strangers to assist for nothing."
506 Thanks
1285 Thanked
Seems like your usually quite happy to give people free advice on a public forum, I don't understand why you are trying to lay in to me. Your clearly a very knowledgeable and helpful chap and Iv'e done nothing but respect everyones advice and knowledge.
I didn't think for a moment that you were, i was referring more, as to how these cables would be routed from the central position to the individual plots... Which you have now cleared up, by you stating that you are following the road.... Are you running this buried cable in ducting, or just direct buried??
Don't be tempted to run 2 core SWA rather than 3 core, using the Armour as the earth, it won't comply with main bonding requirements. To cut costs and reduce cable size, consider using 2 smaller cables in parallel. Direct cable burial over a 150m is going to need a lot of man hours to remove sharp stones and other debris from the cable trench floor and sifting of excavated soil for the first backfill layer after the soft sand. It could well turn out cheaper to duct the cable, which if planned correctly, could provide a means of replacing the cable(s) in the future, should it be deemed necessary....
Oh and if i were you, i'd get everything in writing from this Electrical Engineer you talk about. Is he the guy that produced the cable size print out you posted, because there are a few fundamental data errors on that calculation sheet??
Currently the 10mm cable that the original land owner laid is just direct buried. When we did the excavations on site last month for the turning circle and retaining wall we laid down 30m of ducting from the edge of our plot to the dwelling entrance. For the sake of a few quid we will be laying ducting for the rest of the cable run.
Thanks for that tip regarding laying two cables, perhaps the current 10mm cable could be utilised somehow if it is fit for purpose.
Unfortunately, that would be highly unlikely!! That cable is a dead duck i'm afraid.
May be you can save it, and use for garden/ shed / garage, installations etc...
Reply to New supply from transformer mast for 9 separate metres property connections? in the Commercial Electrical Advice area at ElectriciansForums.net
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
