View attachment 24708

Here is the cable calculation for 10mm cable at 150m - he intimated it would give 25 amps at 5% VD.

The above doesn't make much sense to me.

I don't know much about his design software, but if that's what he's saying then he's wrong I'm afraid, very wrong!

On a 10mm three core thermosetting SWA, 25A over 150m results in a voltage drop of 17.6V, or 7.6%, 2.6% over the maximum allowed for general circuits according to the guidance given in appendix 4 of BS 7671.
 
I don't know much about his design software, but if that's what he's saying then he's wrong I'm afraid, very wrong!

On a 10mm three core thermosetting SWA, 25A over 150m results in a voltage drop of 17.6V, or 7.6%, 2.6% over the maximum allowed for general circuits according to the guidance given in appendix 4 of BS 7671.

Thank you for bringing this to our attention!
 
Having looked closer at that picture, I've so far counted what appear to be at least 9 glaring errors with the software?!

Is anyone else in a position to confirm or dispute?
 
Is this a wind up? It was Friday yesterday.
For someone to buy a plot of land with such obvious problems beggars belief.

As for this being a self-build, it has all the hallmarks of a disaster epic. Lots of money sinking without trace.
 
Is this a wind up? It was Friday yesterday.
For someone to buy a plot of land with such obvious problems beggars belief.

As for this being a self-build, it has all the hallmarks of a disaster epic. Lots of money sinking without trace.

No wind up... what's Friday got to do with it, have no idea what your'e talking about! When my parents bought the land they were naive! They put trust in a NHBC housing developer (who is selling the plots) and the solicitors who dealt with paperwork. Lesson learnt for them, they wont make that mistake again if they buy development land in the future.

I will be glad when the services are sorted, everything else is fully in our control regarding building works. My parents have experience of multi-million pounds worth of building projects.
 
Given the problems with the electricity, water and sewage I would suggest you employ a project manager that knows what he is doing.
Your comment “I’m not running cables for others” is incredibly short sighted. As for your plot having its own potable water and sewage arrangement is bordering on stupidity.

You would seem to have alienated yourself from the other owners and now you’re going to pay for it.
But as it’s your money, do as you will.

I assume you are paying this supposed “engineer” for his services, I find it somewhat offensive that you come here expecting total strangers to assist for nothing.
 
Given the problems with the electricity, water and sewage I would suggest you employ a project manager that knows what he is doing.
Your comment “I’m not running cables for others” is incredibly short sighted. As for your plot having its own potable water and sewage arrangement is bordering on stupidity.

You would seem to have alienated yourself from the other owners and now you’re going to pay for it.
But as it’s your money, do as you will.

I assume you are paying this supposed “engineer” for his services, I find it somewhat offensive that you come here expecting total strangers to assist for nothing.

Water is sorted, we have an individual holding tank that will serve our property if pressure does drop during peak times.

Electricity... well Scottish Power Energy Networks have designed the system, think they know what they are doing...

And we are employing a SEPA drainage expert for the percolation test and drainage reports who will design a suitable system.

Don't think we need a project manager to do that mate, as it's all sorted and in the pipeline.

Why would I run cables for everyone... I'm not the original land developer, I have liaised with SP to identify a possible solution for connecting into the mains electric for everyone. Pretty sure everyone is happy I have done this for people. They aren't expecting me to lay and connect cable to there plots, I have no idea why you think I would do that.

Say you live on a normal street and everyones gates get stolen, are you going to go out and buy and fit everyone new gates... fair play if you are you must be a very generous and kind person...

We are not alienated with any plot owners, some are good friends some I have only met once as we haven't been on the site full time yet. The only person that we are alienated with is the original land developer, who in my opinion hasn't done fully what I expected from him. But life is to short to start a legal battle with him or fall out majorly... he will be one of our neighbours when he gets his lodge built so it's just not worth it!

"I find it somewhat offensive that you come here expecting total strangers to assist for nothing."

11,060 Posts

506 Thanks

1285 Thanked

Seems like your usually quite happy to give people free advice on a public forum, I don't understand why you are trying to lay in to me. Your clearly a very knowledgeable and helpful chap and Iv'e done nothing but respect everyones advice and knowledge.
 
I'm not laying any cable for anyone else... just our own plot.

There is a 10mm cable laid in at the moment, which isn't of any use to us - maybe a temporary supply for plugging in tools - that would be useful and save on petrol with the generator! Max load would be 25 amps as suggested by the engineer and calculations above.

Not crossing any plots, following the road. It has been measured countless times. 115m to the edge of the plot, then another 30m to the entry point in the dwelling.


I didn't think for a moment that you were, i was referring more, as to how these cables would be routed from the central position to the individual plots... Which you have now cleared up, by you stating that you are following the road.... Are you running this buried cable in ducting, or just direct buried??

Don't be tempted to run 2 core SWA rather than 3 core, using the Armour as the earth, it won't comply with main bonding requirements. To cut costs and reduce cable size, consider using 2 smaller cables in parallel. Direct cable burial over a 150m is going to need a lot of man hours to remove sharp stones and other debris from the cable trench floor and sifting of excavated soil for the first backfill layer after the soft sand. It could well turn out cheaper to duct the cable, which if planned correctly, could provide a means of replacing the cable(s) in the future, should it be deemed necessary....

Oh and if i were you, i'd get everything in writing from this Electrical Engineer you talk about. Is he the guy that produced the cable size print out you posted, because there are a few fundamental data errors on that calculation sheet??
 
I didn't think for a moment that you were, i was referring more, as to how these cables would be routed from the central position to the individual plots... Which you have now cleared up, by you stating that you are following the road.... Are you running this buried cable in ducting, or just direct buried??

Don't be tempted to run 2 core SWA rather than 3 core, using the Armour as the earth, it won't comply with main bonding requirements. To cut costs and reduce cable size, consider using 2 smaller cables in parallel. Direct cable burial over a 150m is going to need a lot of man hours to remove sharp stones and other debris from the cable trench floor and sifting of excavated soil for the first backfill layer after the soft sand. It could well turn out cheaper to duct the cable, which if planned correctly, could provide a means of replacing the cable(s) in the future, should it be deemed necessary....

Oh and if i were you, i'd get everything in writing from this Electrical Engineer you talk about. Is he the guy that produced the cable size print out you posted, because there are a few fundamental data errors on that calculation sheet??

Currently the 10mm cable that the original land owner laid is just direct buried. When we did the excavations on site last month for the turning circle and retaining wall we laid down 30m of ducting from the edge of our plot to the dwelling entrance. For the sake of a few quid we will be laying ducting for the rest of the cable run.

Thanks for that tip regarding laying two cables, perhaps the current 10mm cable could be utilised somehow if it is fit for purpose.
 
Currently the 10mm cable that the original land owner laid is just direct buried. When we did the excavations on site last month for the turning circle and retaining wall we laid down 30m of ducting from the edge of our plot to the dwelling entrance. For the sake of a few quid we will be laying ducting for the rest of the cable run.

Thanks for that tip regarding laying two cables, perhaps the current 10mm cable could be utilised somehow if it is fit for purpose.

Unfortunately, that would be highly unlikely!! That cable is a dead duck i'm afraid.
May be you can save it, and use for garden/ shed / garage, installations etc...
 

Reply to New supply from transformer mast for 9 separate metres property connections? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock