Butchering a consumer unit Part deux

Discuss Butchering a consumer unit Part deux in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Staff member
Esteemed
Arms
Supporter
Patron
Reaction score
17,245
Heating system in a local church which is basically tubular heaters under a few pews.

A local company has already quoted thousands to rip all this out and start again. The committee are reluctant to spend massive amounts as the building only gets used for 2 hours once a fortnight.
It’s old, but it all works.
471CB6BF-E147-4C66-AA98-5C7A00053012.jpeg


Main switch on left is always on to power everything here.
The silver box next is a contactor.... will get to that in a minute..
Next is the mainswitch for the fuseboard... they turn this on during the week before a service.... but only sends power to the top of the contactor.
Next is the fuseboard.... 6 fuses across 3 phases going out on the old twin and earths that disappear into the wall below it then go to heaters.
The rightmost MEM switch doesn’t get used. Neither does the circular mechanical time clock below.... which is marked as suppliers clock.
The electronic programmer beside it appears to have replaced another mechanical clock which energises the contactor coil.... the switch below that overrides the programmer.... which is now surplus to requirements as the electronic programmer has its own override button.

So, just to make things a little safer without tearing it all out, could I take the guts out the fusebox and install a DIN rail with rcbo’s?
Leave the box and lid as it is, but fix a Perspex shield with a hole for the rcbo’s to stick through so they can be reset, but all the connections are safely behind the barrier.

6B045797-C179-4E4E-86DD-54AF9D89F9B3.jpeg

Whew... long post.
There’s a fairly modern 4 gang plastic CU elsewhere serving lighting and power, so I’m quoting to change this to rcbo as well.

ps, the other box a foot below the switch is a room thermostat, and if it’s also surplus, it’s coming out for LN.
 
I have no idea why you are intending to create an ad hoc dist board. I would give them two options, divert the supply into an rcd which isn't ideal or completely replace the board. The fact they are not keen on spending too much money would be of no concern to me.
 

Reply to Butchering a consumer unit Part deux in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock