Morning guy's

i am installing a Fronius IG inverter and it states that the max resistance at the ac side from inverter to main service head is max 0.5 ohms, if i have a PME system am i right in assuming the zs at inverter is the zs at board plus max 0.5 ohms for example zs at board 0.35 ohms plus ac cable max 0.5 ohms = max zs at inverter 0.85 ohms

ie max cable cable r1 r1 0.5 ohms


cheers
 
Presumably this is an IG TL inverter? I don't think it's an issue on standard IG inverters.

Are you getting confused between Zs and Ze? Zs will be the reading at the inverter.
 
true zs at inverter ze is actually 0.21 and zs at cu is 0.2 zs at inverter is 0.61 so r1r2 is .41 ish

also i have been using fp cable for ac side is this over the top or a requirement, generally clipped direct, if cable clipped dirct i assume no rcd required

thanx for advice
 
What inverter are you using? I reckon you should look at upgrading that cable - seems undersized to me.
 
If your doing r1r2 with an isolator at cu end the isolator can give you a high reading, I've found this out a few times.
 
Agreed, it was, but i sometimes swap "line" onto another pole and it they been alright - all im trying to say, is sometimes high R1+R2 tested through a closed isolater or two can be a reason for high reading.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fronius IG unit and ac side resistance
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
10

Thread Tags

Advert

Thread statistics

Created
elecsol,
Last reply from
dansk,
Replies
10
Views
1,547

Advert