Hi
A professional electrician installed power to an outside greenhouse about 6-7 years ago. The supply has very recently developed a recent RCD tripping fault. By process of elimination, the overwhelmingly likely place for the fault is a N-E leak in a Prysmian Resin Cable Joints between two SWA cables which I found buried in the greenhouse (and pretty 'damp' on the outside!).

Replacing the joint is a bit of an endeavour, so before getting the work done, I'd like to ask if these joints are known to fail? It 'looks' solid enough, and in many respects I'd be surprised if it has failed as it "looks" well done, and the rest of the installer's work has always been very solid. It gets hot and humid in a greenhouse though...

Cheers
Damien
 
N & E are normally at a very similar voltage so not as prone to shorting out as a result of damp, you would usually see L-E (trips RCD at low levels) or L-N (trips over-current so bigger bang). Resin joints are generally good if done properly and 6-7 years suggests nothing too obviously wrong to begin with.

However, mechanical damage can do that and it could be a stone pushed in to the SWA cable somewhere that is causing it. Do you know if the cable was put in duct or buried direct in the ground? If so, was sand used for initial back-fill?

More obviously, has any digging work taken place close to the run of the cable?

If you have a definite low resistance N-E short there are ways to get a reasonable guess as to where it is, but if it is a modest resistance from a poor (but still bad to have) fault then pinning down where along the cable it is can be almost impossible and you usually have to split at junctions and check which segment is at fault, etc. Obviously having eliminated any accessories first.
 
Did the pro electrician bring the cpc through to the greenhouse or is it a TT.

I was just wondering about the metal framing?
 

Reply to Do Prysmian Resin Cable Joints sometimes fail over time? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I have a customer who lives in a grand old house which suffers from damp. The ground floor sockets (2 different circuits) IR test at around...
Replies
21
Views
8K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...
Replies
22
Views
3K
Hi Everyone Thank you for accepting me into this group. I'm obvoiusly new to this forum so please excuse any mistakes untill I familiarise myself...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock