Still can't see any problem fitting 1.0 mm flex in a plug top without ferrules.
It's not like the terminals are massive nor the grub screw.
 
  • Like
Reactions: DPG
I cut and ferrule them...I'm doing a 3phase board today.

IMG_0994.JPG
 
Well there you go:D
 
I use plain uninsulated ferrules in plugs and other accessories when building equipment in the workshop, but I don't lose any sleep if it's not convenient to do so out and about, as most plugs make a sound connection if the wire is suitably prepared. Some connectors like good quality IECs have conductor protection under the screw anyway and don't need ferrules at all. I first started ferruling in plugs after I saw sparks doing it in Germany in about 1989 when I was on a work experience exchange from school.

Re. RCBO FE flyleads I keep blue 0.75 and white 0.5mm² ferrules in the kit as standard.

Re. tinning ends of fine stranded, I don't like it at all. It makes things look neat but over time the solder cold-flows out from amongst the strands under the pressure of the screw. I've seen tinned ends in choc block go completely slack after a year or two of thermal cycling.
 
  • Like
Reactions: DPG
@westward10

Wilko has already pointed to the regulation which does express all fine-wire should be suitably crimped, I haven't the regs to hand but I am going by memory and previous discussion on this matter, the exception is if the connection device is designed to take fine-wire without it been dressed, plug tops are not designed to accept fine-wire undressed so the regulation applies that they would indeed need a uninsulated ferrule crimp.... insulated tend to have issues fitting in the plug top.

If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.
 
I can upload deta pendant if you like?
But I assure you the flex don't come crimped

Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
 
@westward10
If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.

What about those MK plug tops, you would have to snip off crimped terminals :)

upload_2017-9-14_17-25-36.jpeg
 
A slightly bigger picture :rolleyes:

images
 
@westward10

Wilko has already pointed to the regulation which does express all fine-wire should be suitably crimped, I haven't the regs to hand but I am going by memory and previous discussion on this matter, the exception is if the connection device is designed to take fine-wire without it been dressed, plug tops are not designed to accept fine-wire undressed so the regulation applies that they would indeed need a uninsulated ferrule crimp.... insulated tend to have issues fitting in the plug top.

If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.
Whilst I am not disagreeing the Regulation does not state they should be suitably crimped but "suitable terminals shall be used or the conductor ends shall be suitably treated", whatever that implies. Whether this applies to a plug top or fixed wiring, the latter I suspect.
 
  • Like
Reactions: Dave OCD and DPG
This is the connection instructions from a rewirable plug top and it states nothing of fitting ferrules or the like.
20170914_174817.jpg
 
Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
Back on site tomorrow so I will do
And I use deta all the time
 
Agree with Lucien - it is not good practice to tin the ends of stranded wire if they are being inserted into a screw terminal.

Ferrules in 13A plug-tops? Really?
 
IMG_3041.JPG
IMG_3043.JPG
IMG_3042.JPG
IMG_3040.JPG
IMG_3040.JPG
Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
 
  • Like
Reactions: westward10

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gavin John Hyde

Esteemed
Arms
Patron
~
Joined
Location
Somerset
Website
http://www.sulis-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Sulis Electrical Services Ltd

Thread Information

Title
Functional earth fly leads and rcbos
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
Gavin John Hyde,
Last reply from
PEG,
Replies
48
Views
13,723

Advert