Hi all, I have a three phase 220v delta wiring system but the real voltage is about 240-245V by measuring between the pairs RS, RT, TS. I want to lower it to about 220V so I was thinking to use three auto-transformers 240-220V wired like this:https://i.Upload the image directly to the thread.com/XL6dO2N.png
I expect to find 220V between the transformer outputs, is it right or there is something more to consider?
Thanks Regards
 
  • Optimistic
Reactions: Shoei
Your gunna have one hell of a turn on surge,
Is the supply up to the job ?
And are the breakers the correct type and size for the new load ?
 
Unfortunately I don't think that works, it'll shift the phase but not the voltage. It may work if you connect the transformers in star to create a virtual neutral. I'll have a think tomorrow when I've had less beer and more sleep.
 
???
Why would it not change the voltage ?
Where are you taking the load from ?
What is the load ?
 
What is the 220V supply to be used for? How many kVAs? Mainly 3 phase loads or single phase? Are you bothered about the hum from the transformers? And remember the heat they will produce and thus energy they will consume 'just being a transformer' and when transforming. Are the loads always on or only as required?
 
RE TOP diagram.
Think like a graph scale -- you have moved some of the voltages but they are still 240 apart = FAIL.
(In theory need neutral point -- so common points of transformers can meet)
In practice .. not a standard install so unwise !
 
Ignore my drunken rambling, there will be voltage transformation and a bit of phase shift. dmx is right though, switch on surge would be interesting.
 
Re #1 - Yes you will produce a 3 wire 220V(line voltage) delta supply with this configuration provided that you connect the auto-transformers exactly as you have drawn out.

But as others have asked do you want a 4 wire star supply which will provide you with a phase voltage of 220V with respect to the star's centre node? If you do then if you used auto-transformers/transformers they would have to be connected in a star (all 0 terminals connected together and each 240 primary terminal to a line) and be step-up 140V to 220V (where 245 divided by square root3 = 140V) or a primary to secondary turns ratio of 220/140 = 1 : 1.6

Electrically and economically it is best to use one 3 phase auto-transformer/transformer not 3 separate single phase ones.
 
Last edited:
  • Informative
Reactions: Shoei and Jim_e_Jib

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Lower the voltage of a three phase 220v delta wiring system with auto transformers
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Roman Ceglua,
Last reply from
marconi,
Replies
8
Views
1,759

Advert