its a gravity pumped system. i have a seimens rwb2e timer and iv mixed the wires. from the fcu there are two twe wires on the load side. on the timer there is L N 1 2 3 4 SO ON CABLE ONE THE LINE WIRE GOES TO L BUT THE BLACK WIRE ON THAT CABLE DONT GO TO THE NEUTRAL IT GOES TO NUMBER 2 R 3 BECAUSE THE NEUTRAL IC CONNECTED FROM THE OTHER RETURNING CABLE. IM NOT EXPLAINING VERY WELL. OK 2 CABLES FROM THE LOAD SIDE OF TH FCU. BOTH CONNECTED TO TIMER BUT NOT SURE HOW. ARRRRRRRRHHHHH
 
its a gravity pumped system. i have a seimens rwb2e timer and iv mixed the wires. from the fcu there are two twe wires on the load side. on the timer there is L N 1 2 3 4 SO ON CABLE ONE THE LINE WIRE GOES TO L BUT THE BLACK WIRE ON THAT CABLE DONT GO TO THE NEUTRAL IT GOES TO NUMBER 2 R 3 BECAUSE THE NEUTRAL IC CONNECTED FROM THE OTHER RETURNING CABLE. IM NOT EXPLAINING VERY WELL. OK 2 CABLES FROM THE LOAD SIDE OF TH FCU. BOTH CONNECTED TO TIMER BUT NOT SURE HOW. ARRRRRRRRHHHHH

******IGNORE THIS POST -- DIDN'T SEE TIMER MAKE, HAVE NOW, SO RE-POSTED********

No, not explained very well........

Your timer - L N 1 2 3 4

The T&E from the FCU will go to L and N on the timer. Nowhere else for now.

The 1 2 3 4 will be relay terminals - probably 1-2 and 3-4 - what brand time is it? Photo?

What you then want is a link probably from L to 1 - 2 then probably feeds the Switched L of either water or heating.
Then a link from L to 3 and 4 will feed the switched L of the other of water or heating.

Big BUT, though - don't take that as gospel, as I have no idea WHAT timer you have. All the neutrals should go to N, whatever, and nowhere else.


******IGNORE THIS POST -- DIDN'T SEE TIMER MAKE, HAVE NOW, SO RE-POSTED********
 
Last edited by a moderator:
its a gravity pumped system. i have a seimens rwb2e timer and iv mixed the wires. from the fcu there are two twe wires on the load side. on the timer there is L N 1 2 3 4 SO ON CABLE ONE THE LINE WIRE GOES TO L BUT THE BLACK WIRE ON THAT CABLE DONT GO TO THE NEUTRAL IT GOES TO NUMBER 2 R 3 BECAUSE THE NEUTRAL IC CONNECTED FROM THE OTHER RETURNING CABLE. IM NOT EXPLAINING VERY WELL. OK 2 CABLES FROM THE LOAD SIDE OF TH FCU. BOTH CONNECTED TO TIMER BUT NOT SURE HOW. ARRRRRRRRHHHHH

Dammitall! Just saw you DID say the timer make.

Forget all I just said.

Your wiring plate is

N L 1 2 3 4

So, all neutrals to N

L from FCU to L.

1 is HW OFF
2 is CH OFF
3 is HW ON
4 is CH ON

So, effectively, what you want (as a minimum) is

L from FCU to L on Timer
N from FCU to N on Timer
SL from HW to 3
SL from CH to 4

Any Neutrals should go to N
 
Ok on at the rear of the fcu there are two 2.5 twe cables. One cable goes into the wall and away and the other goes to the timer, but the red live goes to the l position but the black goes to number 3. Then another 2.5 cable comes back and its red goes to number 1 and the black goes to the neutral
 
By d way its a pumped gravity system so there is a cyilinder stat and room stat and pump and a 3 way valve
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
urgent helpplezzzzz central heating mix up
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
m25maintenance,
Last reply from
m25maintenance,
Replies
9
Views
2,176

Advert