Simple call to look at a shower iso that had burnt out. Apparently not for the first time, so I make my first look in the shower itself. Nothing to report. Take apart the iso and discover the picture below. OK, only 6mm so what rating's the shower....hang on....when I opened it there was 10mm inside.....and there's 10mm exiting the CU.....
Up in the loft I discover the circuits been extended with some 6mm, using 2 x cooker CCU's mounted in surface boxes for joining it together.
DIY will always keep me in a pension.

Up in the loft I discover the circuits been extended with some 6mm, using 2 x cooker CCU's mounted in surface boxes for joining it together.
DIY will always keep me in a pension.