Simple call to look at a shower iso that had burnt out. Apparently not for the first time, so I make my first look in the shower itself. Nothing to report. Take apart the iso and discover the picture below. OK, only 6mm so what rating's the shower....hang on....when I opened it there was 10mm inside.....and there's 10mm exiting the CU.....

Up in the loft I discover the circuits been extended with some 6mm, using 2 x cooker CCU's mounted in surface boxes for joining it together.

DIY will always keep me in a pension.

IMAG0453.jpg
 
  • Like
Reactions: 2 people
Classic case, mate.
It must have cost the DIYer/cowboy more doing that way than doing the job properly with a new 10mm[SUP]2[/SUP]... why do they do it? ... just to save 1/2 hour on the installation time ... never mind the fire risk.
 
Common thing to find on a shower isolator when the rocker burns out, setting aside the change in cable sizes. People turn the shower off by the isolator every day and wear the thing out, just need re-educating into learning its not a switch, its an isolator. And can be left on and just use the switch on the shower.
You just have to ask them if they turn their cooker off at the isolator every day.
 
  • Like
Reactions: 2 people
Haha. I know plenty of old duffers that do !!

Yeah, know what you mean. We have all been brought up to turn off things when your not using them, well apart from my kids aparently, house always looks like a christmas tree when i come home.

But worth explaining to people as it can damage most modern showers Triton/Mira as they have phased shutdown to run cool before stopping so the heat left in them when stopped will cook them up and reduce the life of the shower.
 
Just an aside - You know the Crabtree 50A shower pulls, the really great to fit ones, that cost around £10??? Click (Scolmore) make EXACTLY THE SAME under licence, for about £6.
 
  • Like
Reactions: 2 people

Similar threads

R
Replies
2
Views
3K
Australia
SirKit Breaker
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Rockingit

Mentor
Arms
Supporter
~
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Why you don't down-rate shower cables....
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Rockingit,
Last reply from
Rockingit,
Replies
7
Views
1,686

Advert