Good evening,

I was wondering if anyone has seen SWA cleats that would comply with the 18th edition reg 521.10.202 (i.e. not liable to premature collapse etc...)?

The data sheet for cleats produced by SWAonline say they are 'stable' between -350c and 1050c but they are still made of plastic! Not sure that would be what I am looking for. All well and good using a metal plug and screw but surely the cleat with give up first?

Regards
 
Someone can correct me if I'm wrong but I highly doubt it that a firefighter will go into a building that is over 1050 deg C. I doubt their suits can that that temp.
 
  • Like
Reactions: Rpa07 and snowhead
If the cleats fail at 1050c, there isn't going to be anyone anywhere near them at that time, or anytime soon after.
 
  • Dislike
Reactions: CHRIS GINNAW
Plastic is a bit of a Generic term.

Some plastics deform in warm water.
Some plastics have probably been to the Moon and back.

I'm reasonably convinced that SWA's quote about temps is either theoretical or a misprint, I'm not aware of anyone getting below -273c (absolute Zero)
Stability down to -35OC and up to 105OC constant
 
Maybe I'll tie it up with strips of fire fighters suits then.

Sadly I don't have time to write a list of the infinite amount of scenarios I would like to exclude from my question. But you have covered two there... It's not being installed under water or on a celestial body.
 
  • Like
Reactions: DPG
That would make more sense! -35°C - 105°C
 
Plastic is a bit of a Generic term.

Some plastics deform in warm water.
Some plastics have probably been to the Moon and back.

I'm reasonably convinced that SWA's quote about temps is either theoretical or a misprint, I'm not aware of anyone getting below -273c (absolute Zero)
Stability down to -35OC and up to 105OC constant
Ah the joys of Physics :)
 
I have used cleats as normal and where over doorways or would pose a hazard in worse case scenario used a size up with metal band inside. so its not visible.
 
I have used cleats as normal and where over doorways or would pose a hazard in worse case scenario used a size up with metal band inside. so its not visible.
Now that’s a good idea bud. I’ve used the metal band but never thought of hiding it within a cleat.
 
  • Agree
Reactions: Rpa07
Like Gavin I've used some all band, but I used black and put it on the outside.
 
  • Agree
  • Like
Reactions: Wilko and freddo
Any idea of the price of those, larger P clips for MICC are certainly eye wateringly expensive. Though I assume these are steel and not copper!
 
depending on size of the cable. can use some black metal saddles if you got some. can get a bit pricey unless you get a job lot. it doesnt look that good though but at height its quite discreet.
 
run the SWA on the floor.
 
I have used cleats as normal and where over doorways or would pose a hazard in worse case scenario used a size up with metal band inside. so its not visible.

I do exactly the same, except the first SWA of the year last week i did it every third cleat so roughly every 1200.
 
It would help if manufacturers actually kept up with regs updates and developed products to allow us to easily comply with updated editions!
Tray and steel ties all good for commercial, but I can't see a domestic customer going for that look!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA cleats complying to 18th edition?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
AdamSmith86,
Last reply from
freddo,
Replies
25
Views
8,034

Advert