Discuss Control panel - means of isolation - position of isolator in the Industrial Electricians' Talk area at ElectriciansForums.net

S

SteveDoran

I'm currently signing off new machinery and the control panel isolator is on the side of the panel. I've always believed the handle should be on the door so the panel needs to be isolated prior to opening the door since the handle interlocks into the body of the isolator when in the 'on' position. The manufacturer states the panel conforms with the CE standard but I'm more inclined to think the components within the panel conform (shrouded) but the panel does not meet good electrical practice guidance - If the isolator is OK mounted on the side of the panel I would expect to see warning labels on the doors detailing isolator position and live components etc - any thoughts on this would be appreciated.
 
The info you require and need to read up on BS 60204-1 clause 6.2.2, the method you state is only one of a few options available ...also read the exceptions listed too.

TBH if you are signing off panels and questioning these and possible other points then I would suggest you get familiar with the requirements of the BS60204 (part 1 for general requirements) and also depending on what the panel is doing then other dedicated sections may also apply to specific control systems.

If your panel has all the paperwork and CE marks then why are you getting involved; what exactly are you signing off?...possibly the connection between the customers circuit and the panel ???... if so I'd not dig yourself an hole and just limit your signing off to what you have been asked to do.
 
Last edited:
Thanks for your reply. I'm signing off the entire machine complex, mechanical, electrical, safety, efficiency, compatibility etc and the panel was one part of the big picture. I'm always wary of accepting a CE mark as the final compliance statement since the standard is interpreted differently dependant on country of manufacture - UK seeming to be the most stringent and hence my 'wariness'. Does BS 60204-1 clause 6.2.2 basically say it is OK to place the isolator on the side of the panel and not have interlocked doors into the panel? Thanks again, Steve
 
So a panel that trained personnel could reasonably be expected to access without powering down.
You want a door interlocked isolator?

BTW I hate palletizers, bloody temperamental heaps of crap.
 
Thanks for your reply. I'm signing off the entire machine complex, mechanical, electrical, safety, efficiency, compatibility etc and the panel was one part of the big picture. I'm always wary of accepting a CE mark as the final compliance statement since the standard is interpreted differently dependant on country of manufacture - UK seeming to be the most stringent and hence my 'wariness'. Does BS 60204-1 clause 6.2.2 basically say it is OK to place the isolator on the side of the panel and not have interlocked doors into the panel? Thanks again, Steve

I can neither give a definitive yes or no answer, there are 2 pages relating to that clause giving guidance on what methods can be employed and where exemptions can be made if other measures have been taken... I'll re-iterate - you need a copy of the BS60204 IMHO if you are signing off its EC compliant as a second or third party ... Im happy to point you in the right direction but Ill refrain from doing all the research for you as the answer is tailored to each panel design and not a one solution fits all.
 
PS ...If as suggested - trained operators require access to panel without powering down then you can get away with a side mounted interlock if other methods have been employed to ensure direct contact is not an issue, this could be in the formof finger guard style terminals, shields or an integral interlock system that requires an internal isolation switch be operated to allow access to what would have been live parts.

You have to ask yourself if access should be limited to competent Electricians/Engineers or would the nature of the machine require access to a lesser knowledged person for adjustments or reset functions... which then I would query why these haven't been made accessible for the operator without the need to enter the panel.
 
Does BS 60204-1 clause 6.2.2 basically say it is OK to place the isolator on the side of the panel and not have interlocked doors into the panel? Thanks again, Steve
PM me with a gmail address and I'll send you something for reference, it's about 0.5 meg filesize and 128 pages long.
 

Reply to Control panel - means of isolation - position of isolator in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I recently had my 50yr old 100A main panel replaced with a 200A Siemens panel (MC2040B1200EFC). It is the incarnation with the 200A main breaker...
Replies
4
Views
2K
C
Not sure if this is the right place to post this. Please advise if not. A client I have done some work for runs a brewery supply company, mainly...
Replies
20
Views
6K
Hi, I'm a new member; just joined the forum. Thanks for taking the time to read this, would appreciate any advice... My landlady has just...
Replies
23
Views
5K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
E
Hi Guys Just wondering if anyone could help me with this. I have to submit a quotation for a job but its larger than I have done before. The...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock