Have a new 1652B fluke multifunction meter
Nearly returned to fluke as ERR 5 kept coming up on 3 different locations when doing loop test, (this is due to apparently a noisy earth) as i explained to supplier everything unplugged why would this happen? the ANSWER is to get ERR 5 and then use the up/down arrows on meter and it will show the reading anyway. Strange after doing this at next location have not had to do it again. But if you get ERR 5 this is a way of getting a result. hopefully this could be useful to some people owners of FLuke.
 
  • Like
Reactions: 2 people
Thanks, didn't know that, its never happened though, I have a 1654B, but useful to know.
 

Similar threads