I had a nasty thought about a full blown IR test at 500V, might it finish off the VIR, as in cause it to breakdown whereas at 240Vrms its just hanging in there..... Phew what a nightmare.
 
I think you need to step back and look at the difference between disturbing some decoration and flooring or risking the life of your family, or burning the place down, at the absolute minimum an up front RCD in the meantime.

Obviously some work has been done on the circuits as I note that there are two circuits in Brown that presumably the Blues belong too, but two Browns and Three Blues?
 
The 6A with VIR, probably old lights, has a brown as well.

I wonder if it has had an extension or kitchen re-fit hence partly rewired?
It has been partially rewired as nearly all the sockets have pvc 2.5mm in them although mostly red/black. The left hand side of the house however that is mainly the kitchen & one upstairs bedroom is VIR in the sockets. The 32A on the left is the ring with VIR that goes upstairs, however the socket in the bedroom above is pvc!! I would love to be able to see under the floors.
Moving to the right the 6A has two VIR lighting feeds in it, the brown is from a 6A flex to a 13A socket above the CU since removed entirely, it actually fell off the wall as it was glued on 😵‍💫
Moving to the right again the 16A used to have one of the VIR lighting feeds in it, I moved it to the left for safety.
Moving to the right again the 32A is cooker.
Moving to the right again the 6A is a spur to only a bugler alarm.
Moving to the right again the 16A is a spur to the garage that runs along the outside wall low down (Uggghhh), I believe this was added when the previous owner encountered problems powering a hot tub from the garage as they had made such a mess of the ring wiring it very nearly caught fire (there was melting & smoke damage in one socket from arcing). Hopefully now there is no hot tub and the ring is repaired I can restore the garage to it's original internal spur and remove this particular abortion.
There is an extension, single story dining room added quite a long time ago and that is all in pvc.
The few (2-3) light switches I have examined in the rest of the house are all VIR.
 
I think you need to step back and look at the difference between disturbing some decoration and flooring or risking the life of your family, or burning the place down, at the absolute minimum an up front RCD in the meantime.

Obviously some work has been done on the circuits as I note that there are two circuits in Brown that presumably the Blues belong too, but two Browns and Three Blues?
You missed one of the browns, probably the one in the 6A with the two lighting VIR's.
It would be very nice to get an RCD fitted but I have already been trying to get a plumber for the last 2 weeks and frankly finding any professionals is very difficult. Unfortunatly we have landed from space on Mars as we are new to this area and know nobody, neighbours are also faced with similar problems.
 
I'm looking at this picture, so there are three cables into the 6A?

1658052693343.png
 
Must be my eyesight, but I can see three cables into the B32.
There was when I first arrived, the 6A flax to the double socket was in the B32 till I moved it to the adjacent B6, are you looking at the recent picture in this thread after the move was done or in one of my other threads before the move of that wire I wonder.
EDIT
Ahh yes that is the earlier more deadly picture!
If you look at the picture in post#39 this thread that nasty piece of 6A flex has now been removed completely along with the double socket it was feeding. And as described above the 2nd VIR lighting feed has been moved from a 16A to the same 6A as the other lighting feed.
Sorry for the confusion but there were some things that needed doing immediately!
EDIT EDIT
But looking at the closeup in post#17 I think you may be right, it does look like there are 3 pieces of VIR in the 32A, I dont want to disturb it to look closer but I assume this may be a local spur connection.
 
Last edited:

Reply to Moved house into a disaster zone in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
904
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
Hi, My son has just (last week) had a rewire done on his house in Leyland. He has just bought the house but a "domino" type consumer unit was...
Replies
149
Views
12K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock