Hi,
I have a megger power disturbance analyser in a collegues house, it is showning HF noise bursts of up to 2vp-p at about 5 to 10 times a min. What are the normal causes of these? The mains voltage is in spec.
Thanks
 
Most likely originating from a switched mode power supply in a computer, TV or other audio/visual equipment. Some modern white goods also using SMPS now. What's the frequency of the individual HF burst? If its >20KHz then suspect SMPS as the source. This is assuming you don't have any high power radio, TV or radar transmitters (particularly military/RN/RAF) close to the house, or a radio HAM or illegal CB in close proximity.
Sweeping the rooms with a detuned MW radio may be a quick way of locating the offending source.
 
Last edited by a moderator:
Hi,
Thanks for that, the analyser in question is the PDA1 of 1989 vintage and so only states there has been a HF noise event no frequency display or anything else, all the events get printed on a till roll. The house is about 6 miles from Brize Norton and 3 miles from Oxford Airport. I have suggested trying outlets on different circuits and turning the other final circuits off.
 

Reply to Power quality HF noise bursts 2vp-p in the Australia area at ElectriciansForums.net

Similar Threads

Hello, Not an electrician and I currently live in an apartment building. Over the past few years I have been having abnormal problems with my...
Replies
2
Views
709
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
870
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
771
Hey everyone, lately I've been trying almost everything to reduce the electrical noise over my Be Quiet Straight Power 11 850W 80+ Platinum PSU...
Replies
7
Views
2K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock