I'm running some low voltage cable (e.g. CAT6A data cable; coax cable; HDMI cable and speaker cable) to a number of rooms of the house and would like advice on the best way to do this to avoid plastering the cables into the walls - to give me flexibility to remove / pull new cables in the future (if needed) without having to re-plaster.

It's an old 1915 house with thick plaster walls. We'll be lifting the floorboards, running the cable underneath, and then chasing out a channel in the walls up to a new cutout for a 35mm 2-gang knockout box. Each 2-gang knockout box will be fitted with a 4-module euro plate and the appropriate modules e.g. 2 x RJ45 euro module; 1 x ftype euro module; 1 x HDMI cable euro module.

The knockout boxes have 20mm holes, so I am assuming that I can run 20mm conduit from the bottom of the knockout box, down the chased wall channel and then under the floorboards.

My questions are:
  1. What type of conduit to use? Rigid 20mm PVC? Flexible 20mm Conduit? Any particular brands / suppliers recommended?
  2. How do I couple the conduit to the knockoutbox?
  3. Am I best only running the conduit as far as under the floorboards (to stop them being plastered in) or should I try to run them all the way back to 'base'?
    1. The advantage of doing the full conduit 'back to base' would presumably allow me to pull new cable without lifting carpet or floorboards, but this isn't the biggest pain in the world if I need to do it... Having to re-plaster and re-decorate would be a bigger nuisance.
 
I would use 20mm rigid conduit. You can buy couplers to connect them to the boxes. Conduit all the way back would be good if the runs are not too long, but I would be happy with drops to just below the floor.
There is not much difference between makes of conduit, just go with what you can get, the couplers can just be pushed on but its better if you glue them. Whoever supplies the conduit should have the glue as well, its solvent weld type of stuff.
 
What type of conduit to use? Rigid 20mm PVC? Flexible 20mm Conduit? Any particular brands / suppliers recommended?

Either of the two would suffice.
How do I couple the conduit to the knockoutbox?

For PVC conduit you would use either of these adaptors:

Marshall Tufflex MA7BK Black Round Conduit Male Thread Adaptor 20mm, MA7BK - http://www.discount-electrical.co.uk/product.php/1457872/marshall-tufflex-ma7bk-black-round-conduit-male-thread-adaptor-20mm

http://www.discount-electrical.co.uk/product.php/1457885/marshall-tufflex-ma8bk-black-round-conduit-male-thread-adaptor-25mm

You may need some of these too to secure the conduit to the wall:

http://www.discount-electrical.co.uk/product.php/1444089/marshall-tufflex-mmc2bk-black-round-conduit-u-clip-20mm

If you opt for flexible conduit, here's a cheap solution:

Budget NFB-CP21B 20mm Contractor Pack With 10m Polypropylene Flexible Conduit Reel, 10 x Adaptors & Locknuts, NFB-CP21B - http://www.discount-electrical.co.uk/product.php/382195060/budget-nfb-cp21b-20mm-contractor-pack-with-10m-polypropylene-flexible-conduit-reel--10-x-adaptors---locknuts
Am I best only running the conduit as far as under the floorboards (to stop them being plastered in) or should I try to run them all the way back to 'base'? The advantage of doing the full conduit 'back to base' would presumably allow me to pull new cable without lifting carpet or floorboards, but this isn't the biggest pain in the world if I need to do it... Having to re-plaster and re-decorate would be a bigger nuisance.

Running the conduit back to base isn't really a viable option unless it's a very short, straight run. If there are any bends in the run, you would need to fit angle boxes:

Marshall Tufflex 2MRB4BK Black Circular Angle Conduit Box (2 Way) 20mm, 2MRB4BK - http://www.discount-electrical.co.uk/product.php/1457733/marshall-tufflex-2mrb4bk-black-circular-angle-conduit-box--2-way--20mm

The problem is that if you decide to install additional cabling at some future point, you would then need to lift the carpets and flooring to access the boxes which kind of defeats the purpose of installing an underfloor conduit run in the first place! You could always run a draw-wire between your base-point and the point nearest to where your cabling will enter the chase you'll be cutting in the wall, and use that to install any future cables.
 
I would use 20mm rigid conduit. You can buy couplers to connect them to the boxes. Conduit all the way back would be good if the runs are not too long, but I would be happy with drops to just below the floor.
There is not much difference between makes of conduit, just go with what you can get, the couplers can just be pushed on but its better if you glue them. Whoever supplies the conduit should have the glue as well, its solvent weld type of stuff.
You should ALWAYS glue them with the correct adhesive they are NOT push fit. Just imagine the hair pulling heartache if the UNGLUED joits came apart when you are trying to pull cables through, don't bare thinking about, do it once and do it right first time as Mike Holmes would say.
 
For 2 cat5 cables, a co-ax for the ftype, speaker cables etc etc, I would think 2 x 20mm conduit drops per point.

I’m thinking of the capacity of 20mm to take that number of cables. Also got to think of the future if you decide to pull in a new cable alongside existing.
As suggested, make sure the adaptors are glued on.... and if your putting a bend in the conduit you can either buy pre made 90’ bends which have to be glued on as well, or use a bending spring. That is an art form in itself
 
You should ALWAYS glue them with the correct adhesive they are NOT push fit. Just imagine the hair pulling heartache if the UNGLUED joits came apart when you are trying to pull cables through, don't bare thinking about, do it once and do it right first time as Mike Holmes would say.

For surface work I completely agree, but when it's being plastered in such as this scenario the conduit won't move anywhere if it isn't glued
 
You should ALWAYS glue them with the correct adhesive they are NOT push fit. Just imagine the hair pulling heartache if the UNGLUED joits came apart when you are trying to pull cables through, don't bare thinking about, do it once and do it right first time as Mike Holmes would say.
You don't have to always glue conduit and it can be push fit. As long as it is properly supported and secured it will never come apart. Coming apart is only a problem with insufficient saddles, and boxes not fixed, poor workmanship in other words. I rarely glue plastic conduit.
 
You don't have to always glue conduit and it can be push fit. As long as it is properly supported and secured it will never come apart. Coming apart is only a problem with insufficient saddles, and boxes not fixed, poor workmanship in other words. I rarely glue plastic conduit.

Any surface mounted PVC conduit should be glued, with the exception of expansion couplers. PVC conduit moves too much on its own through expansion and contraction to not be fixed together.
I doubt any manufacturer will approve of it being installed without gluing.
 
You don't have to always glue conduit and it can be push fit. As long as it is properly supported and secured it will never come apart. Coming apart is only a problem with insufficient saddles, and boxes not fixed, poor workmanship in other words. I rarely glue plastic conduit.
I’ve got to agree with Pete999 that you should always glue your conduit. Also run redundant conduits with pull strings
 
I’ve got to agree with Pete999 that you should always glue your conduit. Also run redundant conduits with pull strings
Draw strings aren't always necessary over here. I think you tend to install longer runs over there. We have a regulation that asks for adequate means of access (drawing boxes etc) for containment intended for cables to be drawn into.
 
Thanks for the advice, guys.

I am going to go for the 20mm PVC conduit drops from each of the knockout boxes as you suggest. I will run them to just under the floorboards. I will go for 1 per 1-gang knockout box (2 euro plate) and 2 for the 2-gang knockout boxes (4 euro plate).

The HDMI connectors are too big for 20mm conduit, so I am going to go with HDMI mini connectors and then fit mini-to-full convertors on the end.

Good advice about the conduit glue. I will get that done.
 
You don't have to always glue conduit and it can be push fit. As long as it is properly supported and secured it will never come apart. Coming apart is only a problem with insufficient saddles, and boxes not fixed, poor workmanship in other words. I rarely glue plastic conduit.
Not glueing it is also poor workmanship in my opinion.
 
Although I agree that plastic conduit should be glued, there will be no movement if the conduit is buried in plaster.

advise fixing with saddles... the old crampits that could be used will crush the pipe when hammered in.
 
Although I agree that plastic conduit should be glued, there will be no movement if the conduit is buried in plaster.

advise fixing with saddles... the old crampits that could be used will crush the pipe when hammered in.
You would be hard-pressed to fix PVC conduit in a chase with saddles, a bit OTT, neither would I use Metal crampets designed for Metal conduit, either split, or solid conduit with PVC conduit, asking for trouble, I used Plasterboard nails each side of the oval tube to hold it in place whilst the compo set and kept it in place below the finished wall covering, when I was house bashing.
 
If the chase is wide enough, what’s wrong with saddles? No need to bother with the back bar, just nail it in place with felt nails.

To use the clip in fixings, you’de need to cut the chase deeper.
 
I disagree on gluing being essential. It isn't if the conduit is installed correctly, if people are installing plastic conduit so badly that it requires gluing to remain secure then they need to have a look at their workmanship. However I respect the views of others who feel gluing is required even if installed properly, and am not so ---- that I feel the need to plaster other peoples posts with red crosses.
 
However I respect the views of others who feel gluing is required even if installed properly, and am not so *---- that I feel the need to plaster other peoples posts with red crosses.
I hope you accidentally left the 'b' out on that one...…..if not, I worry for you!:(…..but at least you don't use glue.:)
 
I disagree on gluing being essential. It isn't if the conduit is installed correctly, if people are installing plastic conduit so badly that it requires gluing to remain secure then they need to have a look at their workmanship. However I respect the views of others who feel gluing is required even if installed properly, and am not so ---- that I feel the need to plaster other peoples posts with red crosses.
I disagree on gluing being essential. It isn't if the conduit is installed correctly, if people are installing plastic conduit so badly that it requires gluing to remain secure then they need to have a look at their workmanship. However I respect the views of others who feel gluing is required even if installed properly, and am not so ---- that I feel the need to plaster other peoples posts with red crosses.
So it's wrong in your eyes to disagree with someone is it Mate? and I agree that the red cross is a bit BANAL.
So how can I disagree without the red cross? and you consider gluing PVC conduit is only required if the conduit is installed incorrectly do you? Answers on a post caed leave the red crosses out please, it's BANAL
 

Reply to Running conduit in walls to knockout boxes for low voltage cables? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi all my dad was an electrician and did work on my house in the early 2000s , i had plaster wall lights and am now in the process of redecorating...
Replies
4
Views
2K
I had a job today and i’m back at it again tomorrow. The customer wants a new chrome fitted USB socket installed in his kitchen, but the current...
Replies
6
Views
2K
I have a 20mm steel conduit drop to an accessory box buried in the wall. It was previously used for lighting cables and had 2 x 1.5 t+e and 1 x...
Replies
7
Views
2K
Trying to replace a single run, approx 3M with no bends, of a single 1.5mm twin & earth cable between 2 lighting points in a domestic space. Cable...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock