Yes that one where no definition is given for multiwire, fine wire or very fine wire. To me that covers all conductors beyond solid core does it not. Whatever it refers to the requirement is to fit suitable terminals or suitably treat the ends.
IEC 60228:2004?The terms are defined in other British standards and if you look at the data sheets for the cable it should tell you what type and class of conductor it is.
Agree with Lucien - it is not good practice to tin the ends of stranded wire if they are being inserted into a screw terminal.
Ferrules in 13A plug-tops? Really?
Lovin' this...it's been a while since there has been an intense debate, over the minutiae of the trade![]()
Since I've started to use ferrules more, I see more of them in use. I must've been ferrule blind![]()