I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables coming directly from the fuse box.

I've taken a photo of one of the light switches. (attached to post)

1. It has the earth attached to the metal switch box.
2. All the sockets are done the same way.
3. All the conduit for these circuits are metal.

I need an NICEIC certificate for these offices. He has said we will need to rewire everything and there is no way around this.
I am seriously stressed now as this will cost a fortune.
Is this totally correct? If not, does anyone have any other ideas how to get this certified without rewiring?
 

Attachments

  • IMG_4879.jpeg
    IMG_4879.jpeg
    310.8 KB · Views: 32
If the wiring is in metal conduit, then that would (or should) be the earth! Perhaps your "electrican" has not met this type of wiring before, in which case he shouldn't be doing the work!

NB: I once saw a flat needlessly rewired with twin & earth pulled into every metal conduit that was perfectly OK for continued service!
 
Suggest to your electrician that they should check regulation number 543.2.1 in the current wiring regulations, this permits metal conduit to be used as a protective conductor (earth)

The installation will need to be thoroughly tested to ensure that the conduit is still in suitable condition to be the earth for the circuits.
 
If the wiring is in metal conduit, then that would (or should) be the earth! Perhaps your "electrican" has not met this type of wiring before, in which case he shouldn't be doing the work!

NB: I once saw a flat needlessly rewired with twin & earth pulled into every metal conduit that was perfectly OK for continued service!
Thanks SJD, I appreciate the response. Is this 100% okay for 18th edition wiring regulations and should not stop an NICEIC certificate being issued? I think he's saying the fuse box upgrade now means the earth cannot be on the conduit/socket.
 
Suggest to your electrician that they should check regulation number 543.2.1 in the current wiring regulations, this permits metal conduit to be used as a protective conductor (earth)

The installation will need to be thoroughly tested to ensure that the conduit is still in suitable condition to be the earth for the circuits.
Thanks Dave, great to see it in black and white. What would the test involve to ensure it's in suitable condition? Visual inspection and the earth readings?
 
whereabout in UK are you? (First part of postcode will suffice)

Maybe a forum member could give you an 'eyes on' second opinion
 
whereabout in UK are you? (First part of postcode will suffice)

Maybe a forum member could give you an 'eyes on' second opinion
Thanks Littlespark, I have another electrician that I can get down to have a second opinion if needed. If you'd find any more photos useful for this forum post though, let me know what would be useful.
 
I dont think photos will help....

Is the conduit surface or buried in the wall?
Surface, you could easily check if conduit was continuous back to board. Buried? ive seen plenty jobs where the conduit has just been cut and used as a route for running a t&e down to the switch. Either way, its easy to check continuity with the normal test equipment every sparky has.
 
I dont think photos will help....

Is the conduit surface or buried in the wall?
Surface, you could easily check if conduit was continuous back to board. Buried? ive seen plenty jobs where the conduit has just been cut and used as a route for running a t&e down to the switch. Either way, its easy to check continuity with the normal test equipment every sparky has.
It is surface conduit over the top of brick walls. I have been on the roof (flat roof inside a larger warehouse) and it continues over the roof too between each individual office. It's in great condition. I can't confirm if the conduit connects directly to the fuse box but I'm assuming it would just be a matter of replacing the earth cable from the fuse box to the conduit if this section wasn't in great condition?
 
If surface, the conduit might connect directly to the consumer unit... hopefully all from one direction.

If the conduit is buried behind the CU, it might terminate into a large square metal box with the CU in front, relying on just the fixing screws holding the CU onto the box. A big enough earth wire may need to attached to the box and brought into the new CU in addition to this.
 
Wouldn't that connection need to be maintenance free🤔
 
  • Like
Reactions: pc1966
If surface, the conduit might connect directly to the consumer unit... hopefully all from one direction.

If the conduit is buried behind the CU, it might terminate into a large square metal box with the CU in front, relying on just the fixing screws holding the CU onto the box. A big enough earth wire may need to attached to the box and brought into the new CU in addition to this.
It's all surface conduit thoughout the building and surface conduit running to the CU. It's a different type of conduit beside the CU that is older and isn't in as good a condition though. Would the worst case scenario be that a new earth cable is needed to the better condition conduit? (Building was wired in different stages) Or is there any scenario at all where he is correct and it needs rewired?
 
No need to rewire IF the existing cables are in good condition.

It MAY need a partial rewire, in as much as running in an earth wire through the conduit.... but it all depends on how bad the older part of conduit is.... which is why we suggested testing first.
 
No need to rewire IF the existing cables are in good condition.

It MAY need a partial rewire, in as much as running in an earth wire through the conduit.... but it all depends on how bad the older part of conduit is.... which is why we suggested testing first.
Sorry if I'm picking this up wrong, but could we bypass the older conduit with a new earth wire that just connects the CU direct to the newer conduit?
 
Or is there any scenario at all where he is correct and it needs rewired?

If the existing cable is damaged or deteriorated then it may need to be rewired for that reason.

But there is no need to rewire it for not having a seperate earth in there. The worst case scenario for that would be adding an earth wire into the conduit in any part where it is required.
 
  • Like
Reactions: pc1966 and James
You wouldn't bypass it, you would run the earth inside the conduit.
Yep, but I mean you would be bypassing it's use as an earth? And just using the older section purely for holding the new cable?
 
  • Like
Reactions: mainline and pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Circuits earthed on metal box/conduit: Does it need a rewire?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
44

Advert

Thread statistics

Created
Ratmeister,
Last reply from
rewireIT,
Replies
44
Views
5,559

Advert