Was wondering if new regulations require a separate circuit each and an isolator?
No they don't, there is no such regulation, although it would be good practice to do so.
APPENDIX 15 (Informative)
The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable.
This can generally be achieved by:
(i) locating socket-outlets to provide reasonable sharing of the load around the ring
(ii) not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the
ring circuit
(iii) connecting cookers, ovens, and hobs with a rated power exceeding 2 kW on their own dedicated radial circuit
(iv) taking account of the total floor area being served.
433.1.204 Accessories to BS 1363 may be supplied through a ring final circuit, with or without unfused spurs.