Commercial scenario :
lets say 54m , mmm ok 16amp OCPD, mmm ok at 52m I think I will put a 20amp D/P isolator , humour me I will go on . Actually oh dear I've ran out of 4mm T/E , tell you what I will just use 2.5mm instead . Anybody see an issue , cable clear run on open spacious cable tray no influences just straight clear run .
I just know that someone will say it's fine cos 2.5mm will take 25 odd amps .
Conversations requested guys
 
Sorry guys not sure really what you mean . If I've broken some rules then I apologise . Oh and the cable size is after the isolator NOT A FUSED SPUR by the way
 
Lol , don't worry about it , some start posts like this as a wind up , but it has fallen out of favour in the last few days.
 
Oh don't worry about VD it's irrelevent ............ Isn't it . Let's see 2.5mm ooh about 40m max . 4mm what about 60 odd . Oh B type MCB BS60898 Schneider acti 9 10ka . Oh bugger lets just put the last few meters in 2.5mm
 
Hi Dillb . Well this is purely a scenario but I would have thought that the length if you were to carry on from isolator with 4mm then great but this wasn't the question . I've seen lots of installations where other sparks have ran circuit in X cable to an isolator then for some unbeknown reason dropped to cable Y . My question is why not run the whole lot in cable Y if it's ok to use this on the last few meters . I think not . What's your thoughts ?.....??????
 
What???

As long as the neutral conductor can carry the current without overloading then there is no problem
 
Too slow
 
Last edited:
I don't really understand what your point is? Your OP is about 4mm then isolator then 2.5 and now your on about 431.2.1 which is about having a neutral that's CSA is smaller than the line conductor.
 
Last edited by a moderator:
Ok let's rephrase . If calculations show that cable x should be used then how is it ok to use cable Y for the last few metres of this run . I'm not arguing I'm just posing a question that's all . If cable Y could be used for last few metres of said circuit then why are we using cable x for the first bit ?
 
Ok let's rephrase . If calculations show that cable x should be used then how is it ok to use cable Y for the last few metres of this run . I'm not arguing I'm just posing a question that's all . If cable Y could be used for last few metres of said circuit then why are we using cable x for the first bit ?

Probably to meet max Zs figures and permitted volt drop
 
YOu work out your cable calcs on the length and CSA of the conductors used, so if the first 50 meters is 4mm then the final 4 meters is in 2.5mm then you calculate it accordingly.
 
Now your confusing me how can voltage drop be better on a smaller cable at the end of a circuit . Maybe understand if other way round
 
OK ignoring the 431.2.1 reference which appears irrelevant.

If you have a circuit that start in a large csa and then drops to a smaller csa then it is likely that the designer was ensuring that the volt drop limits for the circuit were not exceeded, however you have said that volt drop is immaterial in an earlier post.

Your description of a 54m circuit in 2.5/1.5 would exceed the 11.5 V limit, however if half the circuit were run in 4/1.5 then you may just make the limit.
 
totally agree that you calculate on length and current carrying capacity but if total circuit length equates to using 4mm where and how do you calculate using 2.5 without fusing down at point of isolation .
 
totally agree that you calculate on length and current carrying capacity but if total circuit length equates to using 4mm where and how do you calculate using 2.5 without fusing down at point of isolation .

Then that's what you would use or a cable of a bigger CSA
 
Last edited by a moderator:
I said VD WAS irrelevent being pedantic of course it matters . .ok let's say the circuit is designed on the limit in 4mm , putting 2.5 at end would not be correct . Yes?
 
The whole circuit is suitable for 2.5/1.5 from a CCC consideration, so it is also suitable for 4/1.5 in terms of CCC.
therefore there is no need to fuse down.
The decreased resistance provided by the 4/1.5 serves to reduce the volt drop only.
 
Last edited:
The whole circuit is suitable for 2.5/1.5 from a CCC consideration, so it is also suitable for 4/1.5 in terms of CCC.
therefore there is no need to fuse down.
The decreased resistance provided by the 4/1.5 serves to reduce the volt drop only.
what do you abbreviate to CCC MATE
 
Ok so circuit regarding voltage drop is on limit at end of total circuit we can use 2.5mm for the last few meters ??
 
  • Like
Reactions: 1 person
Ok so circuit regarding voltage drop is on limit at end of total circuit we can use 2.5mm for the last few meters ??

Strewth this is hard work. Only if by dropping the CCC the Zs and VD values comply with the BGB or BYB
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Good one and to think I did Latin at school . In fact they were probably still speaking in Latin when I went to school .
 
Streuth your not wrong . Ok the CCC is fine , Zs is fine but OBVIOUSLY VD WOULD NOT BE BECAUSE OF THE 2.5 add on
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
431.2.1 again
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
43

Thread Tags

Tags Tags
again

Advert

Thread statistics

Created
Jeffmo65,
Last reply from
tazz,
Replies
43
Views
5,737

Advert