F

freedomrun

TN-S. Domestic 1.5 kW shower on a 6mm2 T&E clipped direct for the most part and in some plastic trunking for about 200 cm Total cct length is about 15M. The manufacturers label inside the shower itself states that it is a 9.6kW shower at 230V - should i take this as the power rating or the one also stated as 10.5kW at 240V (now we operate to 230V maybe i should take this as the power rating?) But I refer here to the 10.5kW rating.

Trips out a 32A MCB no problem (DIY installed shower and shower upgraded from previous). Told the customer i've got to include 30mA RCD and increase the MCB size. From what i can work out, the maximum i can go to will be at 46A. I would rather use a lower size cct protection at 40A, but am i likely to find this will trip out with the power rating here.

How much of an issue is the 200cm of cable enclosed in the plastc mini trunking, will this significantly decrease the current rating in this case, or at this length not an problem?

The customer is going to have the hump when i tell him i've got to put Main Bonding in as none present, not keen on swaping out the shower for a less powerful one. Changing the T&E from 6mm2 to 10mm2 is the obvious solution, but wanted to double check the MCB situation - would i be risking it using a 45A MCB on a cct when the regs say 46A is the maximum this cct design can take?
 
Last edited by a moderator:
Best practice rules here , Dont take crap off customers who winge at the cost as its your --- next if all goes wrong . Hes employing you to do it right not DIY it as before , If he dosent like whats best then walk ! , Its suprising how good it feels & i bet he calls you back .
 
  • Like
Reactions: 1 person
in your average gaff, under the floor is reference method B, according to my tables, I seem to remember at college it has something to do with air movement or lack of it
 
Let’s summarise here
All this is only considering the installation method, the regulations, my thoughts.
This does not consider volt drop or any other applicable derating factors.

Cable run 15m of 6mm[SUP]2[/SUP] T&E all installed to reference method B (in my opinion)
Shower 9.6kW @ 230V or 10.5kW @ 240V
Protection device not yet selected.

CCC for 6mm[SUP]2[/SUP] multicore 70[SUP]o[/SUP]C
Ref B 38A
Ref C 46A

Current demand of an instantaneous water heater (no diversity permitted)
9.6kW @ 230V I=P/V = 41.7A
10.5kW @ 240V I=P/V = 43.75A

So in order to carry a current of maximum 43.75A then a 6mm[SUP]2[/SUP] cable must be installed to reference method C and cannot be installed to reference method B.

Questions you have:

Can I use a 45A MCB?

For the shower as an appliance and if the cable were suitable – Yes
For 6mm[SUP]2[/SUP] T&E installed to Ref method B – No (also you cannot use a 40A MCB)
For 6mm[SUP]2[/SUP] T&E installed to Ref method C – Yes

What is the maximum length of trunking before derating is required?

The regulations do not state a minimum length before derating is applied.
You could possibly consider as an electrician that the regulations do give variable derating factors for different lengths of cable in insulation. If you were to apply the same considerations to trunking this would mean that full derating is applied if the length is greater than 50cm. As your length is 200cm full derating would apply.

Solutions available:
Use the 6mm[SUP]2[/SUP] cable as a pulling wire to draw 10mm[SUP]2[/SUP] cable in to replace it, use a 45A MCB, upgrade bonding.

Decide that under the floor is reference method C, remove the trunking, use the existing cable, use a 45A MCB, upgrade bonding.

Read the manufacturers instructions and decide if they specify that you can use any other method of safe installation as these would override the wiring regulations.
 
  • Like
Reactions: 4 people
alternatively, change the shower unit for one with a sensible KW rating. e.g. 8KW.
 
  • Like
Reactions: 5 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on MCB size please - domestic shower cct
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
freedomrun,
Last reply from
freedomrun,
Replies
28
Views
5,429

Advert