Discuss Crabtree C50 breakers. in the Australia area at ElectriciansForums.net
M
monkee
HI all,
what BS number is the crabtree c50, if there is one?
are thay acceptable as PIR reports, say a sub main 16 amp feeding a caravan ( fixed static ) with an old ELCB?
any thoughts
regards P.:crazy:
Hi monkee, The Crabtree C50 MCB is BS EN 60898, NOT BS 3871 as stated by Electro-tech. If your sub-main cable is only rated 16A, then a 50A MCB is inappropriate and needs to be de-rated, Code 1, requires urgent attention, on the PIR.
Check whether a C type is appropriate for the application, they are usually specified when there is fluorescent lighting, small motors etc that may produce switching surges that would operate a B type MCB.
Voltage operated ELCBs do not comply with BS 7671 and should be Code 1, requires urgent attention (replaced by RCD/RCBO) on your PIR.
“Crabtree C50” I think he means the old ones that are black and the size of an old house LOL. I'm not 100% but are they BS 3871 as said.
If this is the C50 range of miniature circuit breakers then yes, they are BS 3871, normally with a short circuit capacity of between 3 and 10 kA.
They are acceptable if the other design parameters are met.
The ELCB was the name given to the early residual current devices and may be acceptable however, if it is a VOELCB (usually has a yellow test button and a terminal marked 'F' or 'Frame') then it should be replaced with a suitably sized RCD.
Reply to Crabtree C50 breakers. in the Australia area at ElectriciansForums.net
I have a holiday caravan which I upgraded to a residential standard lodge. The old static had a 16 Amp supply which was OK as the oven and hob...
7K
Morning All, Having spent many years gleaning information from you all as a non member I've finally needed to join because, try as I might, I...
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
9K
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
6K
Specialist
S
Hi there, I run a small sunbed shop with 2 sunbeds. (please bare with me as I'm not very electrically minded) I have a problem with my sunbed...
11K