Hi,

Quick question, does anyone know if there is a different spec to the U.K. for earth rods?

I'm told in Spain they are longer but not sure if that is correct? Also are there any regs in Spain relating to the positioning of the rods etc (i.e. distance fro property)?

Any advice greatly appreciated as I am new to this forum. :-)
 
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;)

Seriously though, the specs of an earth rod are about its impedance which we refer to as its Ra measurement. In certain ground you need a longer rod to achieve a target impedance than in other types of ground. Factors such as moisture content, conductivity of the soil, overlapping zones of influence, whether the ground freezes and whether you hit the water table would affect how long and earth rod you would need. Also whether you are providing additional protection in the form of an upfront RCD would possible influence how low your rod impedance needs to be.
 
Last edited by a moderator:
  • Like
Reactions: 2 people
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;).

Maybe the spanish fly will extend its potential and increase leakage to an acceptable level
:joker:

Back on topic I know little about Spains electical instalations so cannot advise sorry.
 
spanishrods need to be longer to achieve results as they sleep from 12 noon till 4 p.m.
 
  • Like
Reactions: 1 person
Normally minimum specified by local council but you may have to put 4 in to get the required reading. The reading must be noted of the cert (Boliten) which needs to be issued by a registered Electrician. In on town where i work Spikes are 1.5m go up the road 3km and its 2m. Yes there are many regs regarding TT installs.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
Every install has RCD protection Marvo. Also different rules for different comunidads (counties) the norm is 1.5mm just depends how many it takes to get decent Ra.
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;)

Seriously though, the specs of an earth rod are about its impedance which we refer to as its Ra measurement. In certain ground you need a longer rod to achieve a target impedance than in other types of ground. Factors such as moisture content, conductivity of the soil, overlapping zones of influence, whether the ground freezes and whether you hit the water table would affect how long and earth rod you would need. Also whether you are providing additional protection in the form of an upfront RCD would possible influence how low your rod impedance needs to be.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spanish Earth Road installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Spanish_sunbeds,
Last reply from
mayfair,
Replies
6
Views
3,351

Advert