If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Connected new central heating system,did usual test Zs at switch spur for boiler.Also a visual only on the 3 bed property.Noted no earth on oil supply,upfront a 100ma rcd it's a tt system.Told all this to the gaffer,apparently we did the pit report sometime ago,the client knows all this but failed to do any thing about the issues raised.My query. Is should we have connected the boiler system,there was an existing boiler system already connected,we just connected a y plan new system,who would be responsible if all went ---- up cheers
 
Hi Cliffed

Before doing any additions / alterations all bonding / earthing has to be to current regs, but 'like for like' replacements don't as far as I know. If I'm wrong the other guys will correct me. Was the Zs result OK?

Put your concerns on a Minor Works Cet with your Zs reading


Cheers T&E
 
If the old heating system and new one both connected to the same FCU the changes would be maintenance - and thus upgrades aren't necessary.

However a note on the MWC is in order.
 
If the old heating system and new one both connected to the same FCU the changes would be maintenance - and thus upgrades aren't necessary.

However a note on the MWC is in order.

But you wouldn't have to do a minor works any testing other than a functional test if it was just a change of like for like equipment????
 
then again, you can do a MWC if only to put your concern about the bonding on paper.
 
  • Like
Reactions: 1 person
then again, you can do a MWC if only to put your concern about the bonding on paper.

Not saying you shouldn't it's good practice to do one! Just if it's going to cause issues do what you need and go home. You start doing certs and that could be comebacks.
 
But you wouldn't have to do a minor works any testing other than a functional test if it was just a change of like for like equipment????

Like for like, minimum test is Zs and noted on Invoice. Issues like you highlight would mean raising a MWC
 
Hi Cliffed

Before doing any additions / alterations all bonding / earthing has to be to current regs, but 'like for like' replacements don't as far as I know. If I'm wrong the other guys will correct me. Was the Zs result OK?

Put your concerns on a Minor Works Cet with your Zs reading


Cheers T&E
cheers Zs .33 on tt system ,find ,& noted on report to gaffer
 
  • Like
Reactions: 2 people
Hi Cliffed

Before doing any additions / alterations all bonding / earthing has to be to current regs, but 'like for like' replacements don't as far as I know. If I'm wrong the other guys will correct me. Was the Zs result OK?

Put your concerns on a Minor Works Cet with your Zs reading


Cheers T&E


Is is that what DIY Dave does when he's changing Mrs Jones light or sockets or metal light switches on a non earthed lighting system for a fiver coz Mrs Jones is to tight to pay a proper sparks? I'll have to lend him my loop tester!
 
Is that 33 ohms or 0,33 ohms?? At 0.33 ohms, that's bloody good for a TT system with just one rod in the ground, especially if you have no main bonding on the installation!!

You will probably not need bonding on the oil supply pipe if it's not been buried from the bulk storage tank, ...that you will have to test, to be sure if it's extraneous or not....
 

Similar threads

L
Replies
17
Views
3K
Australia
LlandrilloSpark
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Unsatisfactory
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
cliffed,
Last reply from
Engineer54,
Replies
9
Views
1,550

Advert