Good Evening All. First question on site so apologies for bad formatting.
Am interested to know best work around for testing the off peak side of a split load board fed by a teleswitch meter running economy 7 storage heaters. Able to perform dead tests but no power until after midnight so cannot test Zs or the RCCB that governs the radial circuits. Tenant cannot function test the RCCB either. Other half of split board fed separately from supplier side meter tails.
Any clues or hints very much appreciated - thank you in advance
 
hi would use r1 + r2 value to calculate zs (ze+r1+r2 =zs) as for rcd is no way of testing it unless you go round at midnight just note it on certificate as not tested
 
thank you for reply jaydee81. Sorry for late response, my PC crashed just after posting and is only now working. Thanks again.
 
Take a temporary feed from the daytime flavour board, make sure the radiators are switched off first
 
Thank you for your reply. Can I temporary feed to the intake on the off peak RCCB without it affecting the teleswitch or only to the supply side on the individual radial mcbs? Would ideally like to function test the RCCB whilst i'm there. Do not know anything about how the teleswitches behave only what I have gleaned from this forum.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Economy 7 circuits
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
hitchin72,
Last reply from
hitchin72,
Replies
4
Views
2,422

Advert