fuse size is irrelevent , the pfc is decided by how close the service is to the dno transformer - so even if your cut-out fuse is only 60A your pfc could be as high as 4Ka if youre 400 yrds from a local substation.
if you put 2ka fault through a 1ka mcb - it will operate but cease to work correctly from thence.
in essence , youre choosing a device that will be destroyed after tripping.
And why the manufactures produce 25KA MCB's. eg, ...For use in final circuit installations very close to the distribution transformer as would be found in a sub-station house/building...