Hi,

Just contacted SP energy networks re. a 4kWp installation to see what my options are and was told definitely only G59. However, I see from other threads that there seems to be some leeway when installing slightly over 3.68 if there are no issues with the local infrastructure - the install is on a newly built estate.

I have seen several people referring to G83 stage 2 applications in these situations, but all the info I can find states these are for multiple installs in close proximity - am I missing something here or is it a way of avoiding G59? In which case should I just send in a stage 2 app and see what happens or should I talk to them first?

I appreciate I could probably fit a 16A limited inverter and the customer would benefit from greater output when not hitting the maximum output - can anyone confirm that SP networks are OK with this approach?

By the way has anyone else had problems with the forum search facility - a search for G83 produces no results!

Thanks.
 
The G83/1-1 Stage 2 stuff for >16A is on the Central Networks site which is still up and running and operational using old email addresses since they were taken over by WPD. Whether they still allow it I am not sure. But calling your local DNO as you have is probably the best way of finding what to do.

I could not get search to work yesterday.

Regards
Bruce
 
Some DNOs allow G83 Stage 2 for up to 17kW. You have to ask for permission first and if they say no - then it is G59.

But no consistency across DNOs AFAIK.
 
The G83/1-1 Stage 2 stuff for >16A is on the Central Networks site which is still up and running and operational using old email addresses since they were taken over by WPD. Whether they still allow it I am not sure.

They do indeed. Got a 4000TL going in next week after putting a stage 2 application in a couple of weeks ago. Got a response from WPD within a week saying fine to proceed as long as upper frequency limit is increased to 51.5Hz
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
G83 or G59 for 4 kW install?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
install

Advert

Thread statistics

Created
dougalthedog,
Last reply from
JulianC,
Replies
3
Views
3,739

Advert