If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)
We are looking at getting a professionally installed alarm to keep insurer's happier, and that will need a power feed which (miraculously) we had always planned and the RCBO is in our TPN board ready for it. However, I would rather not have the installers working in there for various reasons even though the quote says "Electrical connection to controls (24hr unswitched, fused outlet) will be supplied by [company]" so I plan to fit an outlet for it.

I was thinking of the MK K963KOALM FCU that has a key-switch and secured fuse holder:

So a few questions for folks on the forum:
  • Am I right that DP switching is normally required for any alarm maintenance, even though they say unswitched?
  • Is the key-switch on that model the same as the MK grid switch units?
  • Anyone know of what screwdriver fits the fuse's security "snake eyes" screw, or if it can be replaced with a normal slotted screw off another MK FCU?
TL;DR How best to feed an alarm panel?
 
For a TN system you just need an unswitched fuse connection unit, intruder alarms tend to have unswitched to prevent unauthorised operation.
 
  • Informative
Reactions: pc1966
For a TN system you just need an unswitched fuse connection unit, intruder alarms tend to have unswitched to prevent unauthorised operation.
OK, so just remove (and lock as needed) the fuse holder out?

In our case the panel and FCU will only be accessible by authorised folk anyway, so 'tamper resistant' is not as important as 'not accidentally switched off by leaning on it'.
 
Yes just remove the fuse and lock off if necessary.
 
  • Like
Reactions: pc1966
The other end of the "Fish Key" that operates the switch should fit the Fuse screw, they'll be one included.
Check second picture on link.
 
The other end of the "Fish Key" that operates the switch should fit the Fuse screw, they'll be one included.
Check second picture on link.
Ah, so simple yet so cunning!
 
  • Funny
Reactions: snowhead
I maybe should have added we have a 300mA delay RCD incomer and the Hager RCBO are SP switching, so I also would prefer the DP switch in case of isolating N-E faults in the unit.
 
I maybe should have added we have a 300mA delay RCD incomer and the Hager RCBO are SP switching, so I also would prefer the DP switch in case of isolating N-E faults in the unit.
Me thinks you over think things😁
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Power for new security alarm
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
pc1966,
Last reply from
pc1966,
Replies
8
Views
1,256

Advert