Cant seem to find info anywhere for bs3871 m1 plug in wylex type b mcb. Anybody know the braking capacity??
also wylex 5a fuse wire pls
Merry christmas
 
Put this into google (wiring matters 29 semi enclosed fuses )and click on the IET link that comes up
It's quicker than me writing them out
 
BS3871 MCB... M1=1ka. M1.5=1.5ka. M3=3ka. etc...
 
  • Like
Reactions: 2 people
Cheers tel. M1 is the one i was looking for.

1ka!!??? pretty low. i guess the main incoming service fuse should cover it if pfc is high.
 
He is!

I had a look at that wireing matters 29 and could not see anything about 3871 mcb;s or is it me !
 
Cheers tel. M1 is the one i was looking for.

1ka!!??? pretty low. i guess the main incoming service fuse should cover it if pfc is high.

no it wont sadly , mcb breaking capacity must match pfc at the CU's terminals.
 
He is!

I had a look at that wiring matters 29 and could not see anything about 3871 mcb;s or is it me !


me neither,what a silly link :26:


(also wylex 5a fuse wire pls)
 
I think you will find if the CU meets EN BS 60439 the CU is rated up to 16 kA as a whole irrespective of the individual componants which vary in domestic boards !
 
I think you will find if the CU meets EN BS 60439 the CU is rated up to 16 kA as a whole irrespective of the individual componants which vary in domestic boards !

that only applies to the internal bus bars , terminals and links within the CU , it does not extend to mcb's which are rated seperately.
 
I think you will find if the CU meets EN BS 60439 the CU is rated up to 16 kA as a whole irrespective of the individual componants which vary in domestic boards !
thats what i always thought. Till biff pi###d on my bonfire.
Got a 100a 1361 type 2 b (33ka)
 
  • Like
Reactions: 1 person
thats what i always thought. Till biff pi###d on my bonfire.
Got a 100a 1361 type 2 b (33ka)

if all mcb's were automatically rated to 16 ka when fitted in a CU why would they all have 2 , 4 , 6 , 10 Ka stamped on the side ?
 
The way I understand
If the board is domestic and not exceeding 100 amp the board is covered by the suppliers fuse, the breaking capacity of the mcbs doesn't have to be greater than the PFC
Over 100 amps or non domestic the above wont apply
 
  • Like
Reactions: 1 person
This subject has been raised a few times and I brought it up at one of the Elex Q & A sessions for that reason.

Its my beleif that the type testing on the CU is up to 16 kA.

Have a look at 530.3.4 .

And that was also the agreed answer from the panel at the Elecx show.
 
The way I understand
If the board is domestic and not exceeding 100 amp the board is covered by the suppliers fuse, the breaking capacity of the mcbs doesn't have to be greater than the PFC
Over 100 amps or non domestic the above wont apply

fuse size is irrelevent , the pfc is decided by how close the service is to the dno transformer - so even if your cut-out fuse is only 60A your pfc could be as high as 4Ka if youre 400 yrds from a local substation.
if you put 2ka fault through a 1ka mcb - it will operate but cease to work correctly from thence.
in essence , youre choosing a device that will be destroyed after tripping.
 
  • Like
Reactions: 1 person
fuse size is irrelevent , the pfc is decided by how close the service is to the dno transformer - so even if your cut-out fuse is only 60A your pfc could be as high as 4Ka if youre 400 yrds from a local substation.
if you put 2ka fault through a 1ka mcb - it will operate but cease to work correctly from thence.
in essence , youre choosing a device that will be destroyed after tripping.

And why the manufactures produce 25KA MCB's. eg, ...For use in final circuit installations very close to the distribution transformer as would be found in a sub-station house/building...
 
  • Like
Reactions: 1 person
Is the 1kA Is or In ? I can never remember.

Also you can upgrade to 16kA 1361s very easily with the little plastic Wylex converter thingy (don't know real name but TLC get them for me).

Laurie
 
In is the tripping current. e.g. 6A,16A,32A, Isc is the short circuit current .
 
just read it twice , says absolutely nothing to suggest mcb ratings are anything other than whats stamped on them.
the reference to bs no is the standardised assemblies for CU's.

Like I said before this issue has raised its head a few times.

GN 3 explains it a bit better than the regs on page 57 .

The BS EN 60439 bit refers to Annex ZA but I can't seem to find that.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
breaking capacity of fuse and mcb
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
goldie,
Last reply from
tony mc,
Replies
23
Views
5,978

Advert